Doors of Disconnects #198571 01/27/11 10:21 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
There are a number of 100 Amp 600V fusible disconnects that were installed on a project. They had installed a round type of voltage indicator (approx. 2" diameter)onto the front face of the switches. The wiring is then secured to the inside of the door with slack and goes to the Line terminals.
My concern is, are we allowed to mount anything on a door? A lot of people did not see anything wrong with it. I don't like it, and was looking for some code articles that I could hit them with. I never installed anything on the door of a disconnect. Thanks

Work Gear for Electricians and the Trades
Re: Doors of Disconnects [Re: SJT] #198573 01/27/11 10:27 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
Modifications to the enclosure (door, etc.) IMHO would be an issue with the UL listing/labeling. Also, I would have an issue with the volt indicators being on the 'line' side; is there any OCP? How are the terminations of the meter leads made on the 'line' side. What purpose were the voltage indicators installed for?



John
Re: Doors of Disconnects [Re: HotLine1] #198595 01/28/11 06:50 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Thanks John,
I don't think it flies with UL. They were installed in the field. I have to check, if there is fuse protection for the meters. The terminations cannot go under the same lug. I want to check that.
They are using them for a fast visual to determine voltage presence.
When I find out, I'll let you know
Good Day - Steve

Re: Doors of Disconnects [Re: SJT] #198596 01/28/11 06:59 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
The set-up seems poorly thought out. One would want the leads to go to the LOAD terminals so that blown fuses -- and single phasing -- would show up.

Further... Is this out in the open? NEMA 3R?

Are you dealing with 1-phase or 3-phase power?

It's hard to see how meter leads would NOT foul up safe access to the fuses.


Tesla
Re: Doors of Disconnects [Re: Tesla] #198616 01/29/11 02:45 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Tesla,
Three-phase, indoor, and they want the leads on the Line side. Large experimental hallway. I agree, the wiring could be in the way.
To be continued, Thanks -SJT


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,437
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
275,537 Are you busy
209,433 Re: Forum
196,830 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3