#197707 12/15/10 03:30 PM
Joined: Jul 2003
Posts: 2
J
New Member
Group,

After the installation of a new product in Italy, we are being told that there is a technical detail that appears not in line with the official recommendation of the European Community.

The power line MUST be located at a minimum of 30 cm up from the floor.

Can anyone provide substantiation of the 30mm claim?

Providing the source would also be a big plus.

Thank you.

James Goedderz
Product Safety Engineer
Tyco/Sensormatic
jgoedderz@tycoint.com

Joined: Jun 2006
Posts: 613
M
Member
Sorry I can't answer that but you just mixed base units 30cm and 30mm
Maybe a bit more info from you too. What power line? the wiring to the receptacle? The receptacle? the cord to the product? All locations, residential , commercial, or Industrial?

Joined: Jul 2003
Posts: 2
J
New Member
Some additional information.

The product is conduit connected, and the concern is the internal hook up terminal block.

We did consider that this might be Italy only, but the notice included the reference to “the official recommendation of the European Community”.

There does appear to be an exception for products that are resistant to water ingress. Ours it not.

The number is 30cm. Commercial environment.

Joined: Jul 2004
Posts: 783
L
Member
I can not give you a specification but I do remember from about 10 years ago, a product we manufactured was modified for use in Germany. One of the requirements was to move the power supply wiring up off of the floor by about a foot. We ended up moving the power components into another free standing cabinet. Our product was electromechanical inspection equipment. Check under the Laboratory equipment standards.

Check out EN61010 and EN60204.

Larry

Last edited by LarryC; 12/15/10 10:04 PM. Reason: found standards numbers

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
dsk 5
Popular Topics(Views)
284,541 Are you busy
217,274 Re: Forum
203,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5