electrical equipment near gas equipment #197354 11/22/10 07:58 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline OP
Member
We know that we cant put meter bases within 1metre of the gas meter, but anyone know of regulations regarding indoor installations and proximity to gas equipment in a normal occupancies, ie not hazardous?

2-322 addresses outdoor installations, I would think there would be as great a concern on indoor installations as well. Building/gas code?

Tools for Electricians:
Re: electrical equipment near gas equipment [Re: jay8] #197355 11/22/10 08:05 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Like a furnace?

Re: electrical equipment near gas equipment [Re: twh] #197367 11/23/10 11:35 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Methane and electricity are integral to my stove top range.

Is that what you're talking about?

BTW, does anyone use natural gas in your province?

I thought 'hydro' was everywhere.


Tesla
Re: electrical equipment near gas equipment [Re: Tesla] #197368 11/23/10 03:17 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline OP
Member
I was referring more to a commercial/industrial environment where there are large gas burning appliances such as boilers.


And yes, natural gas is very common in British Columbia for heating appliances and is often preferred for that application over electric.

Re: electrical equipment near gas equipment [Re: jay8] #197399 11/24/10 06:16 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
The only restricion is related to the vent of the pressure regulator and the gas meter. Most Gas meters have a pressure regulator right beside the meter and the regulator has a vent opening. Electrical equipment that sparks like a receptacle or switch could ignite vented gas. 1 meter separation is all that is required for that.

since there is often an electrical connection to gas appliance I doubt there could be any more restrictions than that. Sure a leaky fitting could cause a hazard but the only restriction is the vent.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,509 Are you busy
209,408 Re: Forum
196,796 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3