electrical equipment near gas equipment #197354
11/22/10 08:58 PM
11/22/10 08:58 PM
jay8  Offline OP
Joined: Jul 2005
Posts: 183
Vancouver, BC
We know that we cant put meter bases within 1metre of the gas meter, but anyone know of regulations regarding indoor installations and proximity to gas equipment in a normal occupancies, ie not hazardous?

2-322 addresses outdoor installations, I would think there would be as great a concern on indoor installations as well. Building/gas code?

Tools for Electricians:
Re: electrical equipment near gas equipment [Re: jay8] #197355
11/22/10 09:05 PM
11/22/10 09:05 PM
twh  Offline
Joined: Mar 2004
Posts: 928
Regina, Sask.
Like a furnace?

Re: electrical equipment near gas equipment [Re: twh] #197367
11/23/10 12:35 PM
11/23/10 12:35 PM
Tesla  Offline
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Methane and electricity are integral to my stove top range.

Is that what you're talking about?

BTW, does anyone use natural gas in your province?

I thought 'hydro' was everywhere.

Re: electrical equipment near gas equipment [Re: Tesla] #197368
11/23/10 04:17 PM
11/23/10 04:17 PM
jay8  Offline OP
Joined: Jul 2005
Posts: 183
Vancouver, BC
I was referring more to a commercial/industrial environment where there are large gas burning appliances such as boilers.

And yes, natural gas is very common in British Columbia for heating appliances and is often preferred for that application over electric.

Re: electrical equipment near gas equipment [Re: jay8] #197399
11/24/10 07:16 PM
11/24/10 07:16 PM
mikesh  Offline
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
The only restricion is related to the vent of the pressure regulator and the gas meter. Most Gas meters have a pressure regulator right beside the meter and the regulator has a vent opening. Electrical equipment that sparks like a receptacle or switch could ignite vented gas. 1 meter separation is all that is required for that.

since there is often an electrical connection to gas appliance I doubt there could be any more restrictions than that. Sure a leaky fitting could cause a hazard but the only restriction is the vent.


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 5
Admin 5
Popular Topics(Views)
244,891 Are you busy
182,003 Re: Forum
172,033 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9677 MB (Peak: 1.1074 MB) Zlib enabled. Server Time: 2018-03-24 11:52:15 UTC