Why TT system has this requirement? #197280
11/18/10 02:15 AM
11/18/10 02:15 AM
T
theseus  Offline OP
Member
Joined: Feb 2008
Posts: 12
china
IEC 60364-4-41-2005

411.5 TT system
411.5.1 All exposed-conductive-parts collectively protected by the same protective device
shall be connected by the protective conductors to an earth electrode common to all those
parts. Where several protective devices are utilized in series, this requirement applies
separately to all the exposed-conductive-parts protected by each device.

What would happen if exposed-conductive-parts collectively protected by the same protective device be connected to different earth electrode?

Tools for Electricians:
Re: Why TT system has this requirement? [Re: theseus] #197297
11/18/10 02:45 PM
11/18/10 02:45 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,348
Estero,Fl,usa
You will see "ground shift" between them. "Earth" is not "zero volts" and you can see differences between ground rods that are surprisingly close together. That is why we always bond all the electrodes in a system.


Greg Fretwell
Re: Why TT system has this requirement? [Re: gfretwell] #197519
12/03/10 11:56 PM
12/03/10 11:56 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,260
SI,New Zealand
Greg,
I agree with the ground shift thing.
IMO, you are wasting time and materials installing Earth Electrodes any closer than about 12' apart.

One thing I have had good results with in the past, is instead of actually driving a second electrode, is clamping some stripped heavy copper wire to the electrode and burying that copper in a long thin trench at about 2' deep, this has bought down the actual earth electrode resistance and hence increased it's current-carrying capacity under fault current conditions.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,566 Are you busy
190,792 Re: Forum
180,520 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.006s) Memory: 0.9523 MB (Peak: 1.0771 MB) Zlib enabled. Server Time: 2019-04-25 10:42:27 UTC