#19718 01/02/03 12:10 AM
F
flush Offline OP
mt question is when do i need a grounging bushing, the one where a ground wire gets luged in the bushing ..... ive done it on commercial jobs but not really sure where i have to ....any code refrence would be good to ....thanks
#19719 01/02/03 03:37 AM
One instance where they are required is when installing conduit or conduit fittings to service enclosures that have KOs, eccentric and concentric. If you were to knock out the largest KO, then I guess it would be the same as punching or drilling a hole, and no bonding-bushing or bonding-locknut is required.
250.92(B)
Use PVC for the nipple or conduit between the meterbase and disconnect/panel and avoid the whole ugly mess.
-Virgil
5 Star Inspections
Member IAEI
#19720 01/02/03 08:06 AM
See 250.97 for voltages greater than 250 V.
They are treated similar to services.