210.52[E],3 #197091
11/08/10 12:10 PM
11/08/10 12:10 PM
K
KJay  Offline OP
Member
Joined: Nov 2007
Posts: 763
MA, USA
Looking over 210.52[E],3 which requires at least one receptacle outlet for balconies, decks and porches of any size, it says the it shall be located not more than 6-1/2 feet above the surface of that area.
So, if this were a GFCI receptacle, would this mean that this is also the maximum height which will meet the readily accessible requirement of 210.8?

2017 / 2014 NEC & Related Books and Study Guides
Re: 210.52[E],3 [Re: KJay] #197093
11/08/10 02:57 PM
11/08/10 02:57 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Kjay:
As I believe the 'change' was to include any size balcony, porch, etc. and the balance of this section remains the same as '08, I would have to say this GFI receptacle would be acceptable at 6'6" max and be readily accessable.



John
Re: 210.52[E],3 [Re: HotLine1] #197108
11/09/10 12:08 AM
11/09/10 12:08 AM
K
KJay  Offline OP
Member
Joined: Nov 2007
Posts: 763
MA, USA
Yes, I see that they took out the square footage and now made it mandatory for all, regardless of size.

So I guess unofficially anyway, it sounds like a GFCI device can be mounted up to 6-1/2 feet high and anywhere between 0-inches to infinity as far as distance is concerned and still meet the definition of readily accessible.

Re: 210.52[E],3 [Re: KJay] #197111
11/09/10 09:39 AM
11/09/10 09:39 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Interesting thought....

Using the defacto info that a receptacle 5 1/2' high or over does not count for resi spacing, and the supposition that utilization equipment cords are 6' from mfg, the 61/2' height would raise concerns. An invitation for extension cords perhaps?

Basically, my point is place a floor lamp with a 6' cord on the balcony, and you cannot plug it in without an extension cord.

Make any logical sense??



John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
djk 2
Popular Topics(Views)
251,556 Are you busy
188,715 Re: Forum
178,426 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.005s) Memory: 0.9601 MB (Peak: 1.0942 MB) Zlib enabled. Server Time: 2018-11-18 04:31:06 UTC