Page 2 of 2 1 2
Joined: May 2005
Posts: 984
Likes: 1
G
Member
It's applicable to both "Dwelling Units" and "Other than Dwelling Units".

This is just going to be SO much fun when you need to install a GFCI for the vending machine.


Ghost307
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Just gave a quick read; I concur with Ghost. Read is 201.8 (A) thru (C) which basically had also had changes, but no exception for the vending machine.



John
Joined: Nov 2007
Posts: 764
K
Member
Thanks. I hope my state kicks this requirement to the curb.

I'm not sure how this new requirement actually solves any real issues, as it seems you could put the GFCI protective device somewhere you need to take an elevator 3 floors up, then walk 5 corridors back to get to and still meet the definition of readily accessible.

I’m wondering if next they are going to make it required to be within sight.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Kjay:
That's going to be a hot discussion at the CEU code change seminars! I'm doing one Tues on new 110.24, as there were a lot of guys interested in AIC/SCA calculations.



John
Joined: Nov 2007
Posts: 764
K
Member
Originally Posted by ghost307
This is just going to be SO much fun when you need to install a GFCI for the vending machine.


I guess it's going to depend on whether your AHJ considers cord and plug connected vending machine equipment, either fastened in place or not, as an obstacle.

Joined: Nov 2000
Posts: 2,148
R
Member
The rule only applies to the GFCI protection that is required by 210.8. The vending machine GFCI protection is not required by the rules i n 210.8 so that GFCI protection is not required to be in a readily accessible location.


Don(resqcapt19)
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Don:
Would you agree that IF the vending machine is in one of the locations called out within 210, then it must be readily accessable?

210.8 (b)(2)(4)(6)(8) ?



John
Joined: Nov 2000
Posts: 2,148
R
Member
John,
That would be a correct statement. As the code expands the locations where GFCI protection is required we will get to the point where the rule for vending machines can be deleted.


Don(resqcapt19)