what is the closes that a receptalce can be to a remote gas pump?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
Is this a "pump" or a "dispenser". The difference is the width of the class 1 div 2 area.
If this is outdoors, a safe answer is 3 feet or greater away, 18" or greater above grade ... If I am reading Table 514.3(B)(1) right. Underground raceways still need sealoffs.