supervisory circuits #195989
09/03/10 10:26 AM
09/03/10 10:26 AM
B
Bravo  Offline OP
Member
Joined: May 2010
Posts: 30
NY, USA
Hello,

I am designing power for an exterior heated enclosure for domestic water piping.

the pwr source will be from stand-by generator circuit.

does the heater have to be supervised?

if so, from where? Fire alarm and/or building management interface panel?

thanks in advance.

Dean

2017 / 2014 NEC & Related Books and Study Guides
Re: supervisory circuits [Re: Bravo] #195992
09/03/10 12:24 PM
09/03/10 12:24 PM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 303
Ogden, Utah, USA
An overall picture of why you are heating the system would help any replies.

And welcome to ECN.

Shane

Re: supervisory circuits [Re: sabrown] #195993
09/03/10 12:56 PM
09/03/10 12:56 PM
B
Bravo  Offline OP
Member
Joined: May 2010
Posts: 30
NY, USA
to keep the pipes from freezing. It is a aluminum enclsosure (HB8E-D) with dual 1900W heating elements. The circuit is fed from stand-by generator distribution.

not to be pointed in right direction for nfpa supervisory ckts.

thanks

Re: supervisory circuits [Re: Bravo] #196006
09/03/10 11:56 PM
09/03/10 11:56 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
Dbravo:

Welcome to ECN forums.

Additional information on the project is required;

Why are heaters required, other than freezing? What type/use group of structure/building?

Is the gen a legally required system, or is it an optional system?

Supervisory circuit to bldg mgt sounds like a good move. The FACP? Perhaps, if the water is destined for fire supression use.

More info will get you more answers and opinions.



John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 7
Popular Topics(Views)
249,346 Are you busy
187,280 Re: Forum
176,630 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9601 MB (Peak: 1.0931 MB) Zlib enabled. Server Time: 2018-09-21 17:40:31 UTC