Gas pipe bond wire splicing #195490 08/05/10 09:53 PM
Joined: Jul 2007
Posts: 4
G
G_Skinner Offline OP
New Member
To make a long story short there was a lightning strike and a fire from some CSST gas line.
The fire investigators removed part of the bond wire and now I need to reconnect it. I can not run back to the electrical service so I need to splice the wire. It is #6 bare solid copper. Am I restricted to a non reversible splice as a ground wire to a ground rod would be or can I use any type of splice?
The irony is I was required to install the bond wire when I wired the house but everyone including the fire inspectors agree that the fire would not have happened if the bond wire was not installed. The lighting followed the wire to the gas pipe.

Thanks
George Skinner

Work Gear for Electricians and the Trades
Re: Gas pipe bond wire splicing [Re: G_Skinner] #195491 08/05/10 11:40 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
Any listed splicing method should meet the requirements of 250.104(B).
If you have some local requirement beyond that, coordinate with the AHJ.


Greg Fretwell
Re: Gas pipe bond wire splicing [Re: gfretwell] #195492 08/06/10 12:06 AM
Joined: Jul 2007
Posts: 4
G
G_Skinner Offline OP
New Member
From reading that section it does not specify any splicing method.

Re: Gas pipe bond wire splicing [Re: G_Skinner] #195493 08/06/10 12:59 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
Exactly, so that kicks you back to 110.14(B)
Quote
(B) Splices. Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose.
Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use.


Greg Fretwell
Re: Gas pipe bond wire splicing [Re: gfretwell] #195494 08/06/10 01:09 AM
Joined: Sep 2006
Posts: 155
C
crselectric Offline
Member
was the gas bond in series with the ufer or rod, I ve always thought the pipe bonds should be supplemental, and not the shortest path to earth. I do solar in n. california and we always have to run a gec from our system to the main gec, but sometimes the path is quite long and I've wondered where lightning current might actually go?

Re: Gas pipe bond wire splicing [Re: crselectric] #195496 08/06/10 07:42 AM
Joined: Jul 2007
Posts: 4
G
G_Skinner Offline OP
New Member
The gas bond was a separate wire from the gas pipe directly back to the service panel ground. It is about 60 to 70ft long as the gas pipe enters at the opposite end of the house.

Back to my question, does the splice need to be non reversible?

Thanks

Re: Gas pipe bond wire splicing [Re: G_Skinner] #195498 08/06/10 12:06 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
I say no. It is just a bond wire and you can use any listed splicing device like a split bolt.


Greg Fretwell
Re: Gas pipe bond wire splicing [Re: gfretwell] #195499 08/06/10 01:53 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Since this is posted in the general subjects area I will offer the Canadian Code answer.
Bonding may be done with any approved connector, Including split bolts, marretts, 2 lugs and a bolt. Crimp or thermit welding and brazing are OK but not required.
Note that the CEC does not allow solder as a connecting material on bonding wires.
Ground wires cannot use split bolts or other removable connections.
So in Canada the bonding wire to the gas pipe can be spliced in any approved manner which I believe is consistent with the NEC.

Last edited by mikesh; 08/06/10 01:54 PM.
Re: Gas pipe bond wire splicing [Re: mikesh] #195501 08/06/10 02:14 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
I agee with Greg, and most of what Mikesh "up north' said, except for "marretts" as I have no idea what that is.



John
Re: Gas pipe bond wire splicing [Re: HotLine1] #195504 08/06/10 05:02 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Sorry, Marrettes are wire nuts made by Marr. It is like saying Kleenex to describe tissue for blowing your nose. You know the coiled spring in an insulated plastic cone that is used to splice wires. Funny how we call Romex, Loomex. For the last 10 years on the tools I always used wire connectors made by Ideal Industries so why don't I call wire nuts Ideals?
Of course there are not too many wire nut companies that make one for 2 number 6 wires.

Originally Posted by HotLine1
I agee with Greg, and most of what Mikesh "up north' said, except for "marretts" as I have no idea what that is.


Last edited by mikesh; 08/06/10 05:03 PM.
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,722 Are you busy
209,640 Re: Forum
196,985 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3