#195483 - 08/05/10 05:42 PM Motor fusing  
Davo  Offline
New Member
Joined: Mar 2010
Posts: 5
Toronto, Canada
I just got back from a booster pump re-and-re. The new pumps are 3 25 HP 575V pump assembly with control - each pump is labeled with a 22.2A draw. The engineer drawings are specifying that we are to supply 3-#6 to the 3-pump assembly fused with a 80A time delay fuse. Looking immediately at table 13 - an 80A fuse is too large for #6 T90. Yet then there is 28-200(d) in the CEC. Here is my question - given that you can up a fuse size to 225% of the motor FLC if it does not start, does the conductor size have to be increased accordingly? It does not mention this a far as I can see in the CEC.

I realize on the face of it, that it appears the engineer didn't consult the code - I would size the conductor normally (22.2 * 1.25) + 22.2 + 22.2. = cable #4. It appears that one motor is a backup only and may not be used at all unless another is manually disconnected.


Last edited by Davo; 08/05/10 05:49 PM.

Tools for Electricians:

#195484 - 08/05/10 06:03 PM Re: Motor fusing [Re: Davo]  
Davo  Offline
New Member
Joined: Mar 2010
Posts: 5
Toronto, Canada
On a second look at the CEC all appears fine as long as only two motors are connected to operate at once - following 28-204(c) up to 300% of the conductor rating is permitted.


#195516 - 08/08/10 02:21 AM Re: Motor fusing [Re: Davo]  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,217
SI,New Zealand
Davo,
What sort of system is this if it supplies a 575V motor?
Just inquisitive there mate.


Let's face it, these days if you're not young, you're old - Red Green grin

#195531 - 08/09/10 03:04 PM Re: Motor fusing [Re: Trumpy]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
I will reply to Trumpy first. 347/600 is the nominal system voltage. Very common in Canada and usually used where 277/480 is used in the US.
So to Davo 28-204 is the right rule and you are applying the right conditions. 125% if the largest motor with the FLC of each additional motor that must be able to run at the same time = wire size. The overcurrent rules allow a breaker as big as necessary provided it does not exceed %300 of the ampacity of the wire feeding the lot.
So 50 amp wire could have a breaker up to 150 amps. If you use #6 r90 then up to 190 amps, not 200. You probably have to start with a max of 100 amp breaker unless it trips, which lets you go up from there.



Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.004s) Memory: 0.7609 MB (Peak: 0.8936 MB) Zlib enabled. Server Time: 2017-08-22 22:38:53 UTC