flexible conduit repair #195391 07/29/10 11:25 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline OP
Member
Anyone know of an approved product that can be used to repair broken/separated flexible metallic conduit? I have a 4" flex with 500mcm feeders to switchgear with the flex broken. So I am hoping I can repair in place without shutdown, remove,replace flex, repull, reterminate, etc etc.

Work Gear for Electricians and the Trades
Re: flexible conduit repair [Re: jay8] #195394 07/29/10 11:35 PM
Joined: Apr 2002
Posts: 7,105
HotLine1 Offline
Member
Jay:

There is no product that I know of for what you described.

Looks like an R&R job


John
Re: flexible conduit repair [Re: HotLine1] #195398 07/29/10 11:46 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
The first question would be how was it separated in the first place. You may have a physical damage problem that precludes FMC.
I have seen people weave this stuff back together but I still would not try it hot. This was not uncommon under computer room floors. I even had a picture in the IAEI magazine of that. Joe T may still have it on his web site in the violations area.


Greg Fretwell
Re: flexible conduit repair [Re: gfretwell] #195405 07/30/10 07:06 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Such damage, presumably within the Electrical Room, is very disturbing.

I rather suspect that the flex was buckled during the original installation.

Alternately, the custodian/owner has been stacking 'stuff' on top of the flex until failure.

We've all seen it: the E Room becomes the closet to jamb everything under the sun for the custodian.

I see an R&R in your future.


Tesla
Re: flexible conduit repair [Re: Tesla] #195409 07/31/10 01:41 AM
Joined: Mar 2007
Posts: 404
noderaser Offline
Member
Duct Tape :P

Re: flexible conduit repair [Re: Tesla] #195459 08/03/10 10:34 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline OP
Member
It was likely due to installation damage since its location makes it unlikely to be hit. It was a little tedious but I was able to wind it back together since it was fairly close to the connector, which saved quite a bit of grief. I knew there were approved kits to repair in use underground conduit, so I was fishing for something similar for flex. thanks for the feedback - i will save the duct tape repair idea for another time.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 23
GeneSF 8
Popular Topics(Views)
257,933 Are you busy
193,663 Re: Forum
183,281 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3