ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Recall notice: Southwire wi-fi wall switches
by sparkyinak. 03/15/18 06:03 PM
Goodman Manufacturing Recalls Modular Blowers
by Admin. 03/13/18 10:40 PM
MAAX Spas Recalls Hot Tubs and Swim Spas
by Admin. 03/13/18 10:29 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 16 guests, and 6 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Above ground pool 680.26 (C) #195337
07/26/10 09:55 PM
07/26/10 09:55 PM
HotLine1  Offline
Joined: Apr 2002
Posts: 6,934
Brick, NJ USA
I'm looking for some info regarding the 680.26 (C) water bond for [u][i][b]above ground pools.[/b][/i][/u]

NOT how to comply with 680.26 (C)...but,

Who supplys and/or installs the bonding point?

Who is paying for that additional work?

If us ECs are having to provide it, any issues with finding the part?

Any other comments appreciated

Last edited by HotLine1; 07/27/10 02:23 PM.

Work Gear for Electricians and the Trades
Re: Above ground pool 680.26 (C) [Re: HotLine1] #195346
07/27/10 01:30 PM
07/27/10 01:30 PM
SteveFehr  Offline
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
I've got an inflateable aboveground pool we set up for my kids in the summer. Does NEC *really* require an equipotential grid be laid down before setting it up, and a ground electrode draped over the side? I mean, it seems absurd, but it sure looks like it; they even go out of their way to say this chapter applies to storeable pools as well as permanant.

To answer your question; pretty sure the pool guy will install the ladder, and possibly the bond as it SHOULD come designed for code-compliant bonding. If he doesn't supply the bond, you would have to. The customer will pay for it all.

Re: Above ground pool 680.26 (C) [Re: SteveFehr] #195347
07/27/10 01:43 PM
07/27/10 01:43 PM
gfretwell  Offline

Joined: Jul 2004
Posts: 9,184
No "storable" pools are not covered by chapter II of the NEC. See Chapter III. The main issue is that you are using all "storable pool" equipment. It should be so marked.
This is all double insulated and the pump comes with a long cord (25')

Ladder cups usually get installed by the guy shooting the concrete and they usually do all of the concrete encased bonding around here. This may be inspected by the structural inspector but there is an "electrical" box to be signed off on the permit so it really should be an electrical inspector. These days most inspectors are multi-rated.
Departments protect licenses when times are tough and the more licenses you have, the better chance you have to keep your job.
The way it worked on my pool was I saw an electrical and a structural inspector before the pool was shot and the electrical inspector did the final. (verifying the fence/cage, alarms etc along with the electrical finals)

Greg Fretwell
Re: Above ground pool 680.26 (C) [Re: gfretwell] #195353
07/28/10 02:46 PM
07/28/10 02:46 PM
SteveFehr  Offline
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Ah, good! I missed the chapter headings. NEC needs to use multiple font sizes or outline-style indents or something; it's often hard to read.


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 5
Admin 5
Popular Topics(Views)
244,411 Are you busy
181,526 Re: Forum
171,577 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9606 MB (Peak: 1.0953 MB) Zlib enabled. Server Time: 2018-03-19 18:23:59 UTC