15 amp circuits commercial? #195178 07/15/10 01:00 AM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
I am looking at a plan for an auto parts store, it calls for lighting to be 20A ckts and gen outlets to be 15A, along with exhaust fans, printer ckt. Isn't there a code requiring all commercial lighting and plugs ckts to be 20 Amps? Or is that just how I've always done it?
Thanks guys,
H20

Last edited by watersparkfalls; 07/15/10 01:00 AM.
2017 / 2014 NEC & Related Books and Study Guides
Re: 15 amp circuits commercial? [Re: watersparkfalls] #195182 07/15/10 02:03 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
H2O:
There are no NEC requirements for 'general purpose' comm receptacles, spacing or ampacity.

However, you may have something in your local codes. Otherwise this is a design issue.

Now, talking about what I call "normal trade practices" comm work would be all #12 & 20 amp circuits; that's how I did it, but that's not NEC for GP circuits.



John
Re: 15 amp circuits commercial? [Re: HotLine1] #195184 07/15/10 04:47 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
I would add to what John has said that using 15a. circuits for receptacles you will be looking at no more than 10 receptacles on a circuit (assume non-continuous), continuous load would only allow 8 receptacles on a 15a. circuit.


George Little
Re: 15 amp circuits commercial? [Re: George Little] #195214 07/18/10 06:27 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
With my AHJ...

#12 is the smallest conductor permitted in Commercial Construction -- to include Romex -- and to include motor loads.

With such a local rule -- no commercial design uses 15 Amp breakers normally. No cost savings are to be had -- instead you end up using more breakers and circuits to handle the total load.


Tesla

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,727 Are you busy
209,644 Re: Forum
196,989 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3