#194707 06/16/10 03:26 PM
Joined: Mar 2005
Posts: 240
Member
I have a wellhead 320 feet from pump house, I am using USE #4 aluminum in a trench not in a raceway...should I tape the wires every 20 feet or so to ensure the cancelling effect or isn't this an issue?
Thanks, H20

Last edited by watersparkfalls; 06/16/10 03:26 PM.
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Mar 2003
Posts: 849
Y
Member
300.3 (B) I don;t think the taping is a requirement.

Joined: Nov 2007
Posts: 763
K
Member
Isn't the USE a triplex assembly or something similar that is already factory twisted?
If not, I can't say that I've ever pulled individual USE conductors before, but I think the twisting is more so that it can be considered a cable assembly and for installation convenience.
Years ago, where I worked at the time, it was common to direct bury individual service conductors and we never had any issues with not twisting the conductors in the trenches, although we did basically lay them right on top of one another anyway.
I couldn't see where it would hurt to twist them though if you wanted.

KJay #194717 06/16/10 11:00 PM
Joined: Mar 2005
Posts: 240
Member
Thanks, KJ and Yoop. They are single strands of AL USE wire.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Trumpy 9
NORCAL 5
Popular Topics(Views)
300,508 Are you busy
230,151 Re: Forum
214,962 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5