#194707 06/16/10 04:26 PM
Joined: Mar 2005
Posts: 240
Member
I have a wellhead 320 feet from pump house, I am using USE #4 aluminum in a trench not in a raceway...should I tape the wires every 20 feet or so to ensure the cancelling effect or isn't this an issue?
Thanks, H20

Last edited by watersparkfalls; 06/16/10 04:26 PM.
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Mar 2003
Posts: 849
Y
Member
300.3 (B) I don;t think the taping is a requirement.

Joined: Nov 2007
Posts: 764
K
Member
Isn't the USE a triplex assembly or something similar that is already factory twisted?
If not, I can't say that I've ever pulled individual USE conductors before, but I think the twisting is more so that it can be considered a cable assembly and for installation convenience.
Years ago, where I worked at the time, it was common to direct bury individual service conductors and we never had any issues with not twisting the conductors in the trenches, although we did basically lay them right on top of one another anyway.
I couldn't see where it would hurt to twist them though if you wanted.

KJay #194717 06/17/10 12:00 AM
Joined: Mar 2005
Posts: 240
Member
Thanks, KJ and Yoop. They are single strands of AL USE wire.