NEC ART 110 working space clearance #194629
06/14/10 01:59 PM
06/14/10 01:59 PM
B
Bravo  Offline OP
Member
Joined: May 2010
Posts: 30
NY, USA
I have 2 existing panelboards rated 208/120V 225A that have to be relocated. To minimize cost and shut-down time,
I was going to covert the existing panelboards into junction boxes and pipe feeder and branch circuits to new panleboard location.

Do the new junction boxes have to conform to NEC ART 110.26(A)(1)?

The existing panelboards are mounted to a brick wall, with a new handicapp lift in front of it.

thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Re: NEC ART 110 working space clearance [Re: Bravo] #194631
06/14/10 02:10 PM
06/14/10 02:10 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Hmmm...with the lift in front, that may be a problem. Boxes have to be accessable.



John
Re: NEC ART 110 working space clearance [Re: Bravo] #194634
06/14/10 02:30 PM
06/14/10 02:30 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 959
Chicago Illinois USA
Maybe, but 314.29 may still bite you in the butt if that ADA lift is in front of them.

Remember that nowhere in the NEC does it state that the rules can be waived if there is a desire to save money or work quicker.

It's probably best to run it past your AHJ before you hang your hat on it.


Ghost307
Re: NEC ART 110 working space clearance [Re: ghost307] #194677
06/15/10 11:25 PM
06/15/10 11:25 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Can you raise or lower the lift and get at the boxes? That way they might not be "readily" accessible, but you are still able to get at them if you move the lift or something like that. Just a thought.

Re: NEC ART 110 working space clearance [Re: harold endean] #194691
06/16/10 12:19 AM
06/16/10 12:19 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,302
Estero,Fl,usa
The only requirement for "accessible" is you don't have to damage the building finish to get to it. How many J boxes have you worked on that you had to move furniture or crawl on your belly in an attic, all perfectly legal.


Greg Fretwell
Re: NEC ART 110 working space clearance [Re: gfretwell] #194700
06/16/10 02:14 PM
06/16/10 02:14 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 959
Chicago Illinois USA
Agreed, but take a look at the ADA lift first and make sure that you can even get to the box once it's installed. I've seen a lot of lifts where the support frame is completely solid.


Ghost307
Re: NEC ART 110 working space clearance [Re: ghost307] #194704
06/16/10 02:23 PM
06/16/10 02:23 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
I should have added..."checck with your local AHJ" to my original reply.

Not being able to 'see' the situation makes for a tough call.



John
Re: NEC ART 110 working space clearance [Re: HotLine1] #194735
06/17/10 08:36 PM
06/17/10 08:36 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
This is definitely a scenario which needs to be verified with the Building Department (any AHJ involved).

Basically, since the existing Panelboards are now Junction Boxes; the need to examine, adjust, service or maintain the Live Circuitry inside is not likely - as compared to a Panelboard, etc.
This, by its self, is open to wide interpretations!

So if the existing "Panelboards-Now Junction Boxes" must comply with 110.26, this will be "Condition 2" - since the ADA Lift assembly is mounted in front of the Junction Boxes.
Condition 2 places 36" minimum between the opening of the J-Box Panelboards, and the closest edge of the ADA Lift.

If the scenario must comply per 110.26 - condition 2, Pullboxes or Wireway Sections mounted above the ADA Lift (or above ceiling, over to a side of the lift, etc.) might be the next best option.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,518 Are you busy
188,690 Re: Forum
178,391 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.004s) Memory: 0.9957 MB (Peak: 1.1622 MB) Zlib enabled. Server Time: 2018-11-16 22:54:34 UTC