Sizing contactors for transformer loads #193964
05/01/10 10:36 PM
05/01/10 10:36 PM
bigpapa  Offline OP
Joined: Mar 2006
Posts: 81
How do you size a contactor that is in the primary circuit of a transformer?
I am looking for a specific CEC rule or guidance.
In this case 75KVA 600V 3PH primary with upstream 70A circuit breaker.

I know you can use definite purpose contactors but i think you have to upsize them for inductive loads. If that is the case, does the code address this specifically?

Tools for Electricians:
Re: Sizing contactors for transformer loads [Re: bigpapa] #193967
05/02/10 01:46 PM
05/02/10 01:46 PM
Yoopersup  Offline
Joined: Mar 2003
Posts: 840
2008 NEC Article 450 450.3 (B).
See Table 450.3(B).
The way I usually do it (if no charts handy).
480 primary/120-208 secondary.
480x1.73 = 830.4 round out to 830
208 x 1.73 = 359.84 round out to 360
75 x 1000 = 75000 Divided by 830 = 90.36 amp pri.
7500 divided by 360 = 208.33
Pri can be up to 250% if seconday protected no more then 125%
So 70 amp breaker Pri. Fine
Secondary 125% x 208.33 = 260.4 amps
See (450.3 (B) Table note 1.
Then go to 240.6.
Thats the way I;ve done it.

Re: Sizing contactors for transformer loads [Re: Yoopersup] #193969
05/03/10 12:54 AM
05/03/10 12:54 AM
twh  Offline
Joined: Mar 2004
Posts: 928
Regina, Sask.
I don't see a rule about controlling transformers, so 14-400 should cover it.
14-400 Control devices shall have ratings suitable for the connected load of the circuits that they control and, with the exception of isolating switches, shall be capable of safely establishing and interrupting such loads
I wouldn't think the transformer is the load. Rather, it has a load. If you connect only capacitors to the transformer, doesn't the primary have a leading power factor like a capacitor and not a lagging power factor like a motor?


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,700 Are you busy
181,815 Re: Forum
171,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9516 MB (Peak: 1.0780 MB) Zlib enabled. Server Time: 2018-03-22 17:56:21 UTC