feeder sizing #193792 04/20/10 12:50 AM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
how should I calculate generator feeders? I have a 17 KW generator 71 amps, 310.15 allows #4 for 100 amps, but does it allow #6 for 71 amps? Do I size according to 310.16 which is still #4?
Thanks,
H20

2017 / 2014 NEC & Related Books and Study Guides
Re: feeder sizing [Re: watersparkfalls] #193795 04/20/10 02:32 AM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Online Content
Member
You can only use 310.15(B)(6) if this is a main feeder for the entire dwelling, basically an extension of the service entrance from a disconnect. That is, by definition, a #4 minimum. In no case could you interpolate down to a #6.
Any other application has to use 310.16.


Greg Fretwell
Re: feeder sizing [Re: gfretwell] #193802 04/20/10 11:46 AM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
thanks Gfretwell


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,207 Are you busy
206,095 Re: Forum
194,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3