EGC Bond in Transfer Switch (Code) #193637 04/11/10 11:17 PM
Joined: Apr 2010
Posts: 5
G
George393 Offline OP
New Member
A customer requests an addtional circuit (3 outlets) in a stand alone garage.

She has an outside 100 AMP disconnect at the entrance. From there the feeder goes direct to the oposite side of the house and terminates at a Ronk 100 AMP manual transfer switch (for a portable generator hookup).

EGC and all neutrals from the single house distribution panel and the stand alone garage distribution panel are bonded together inside the Ronk manual transfer switch. The house distribution panel and the stand alone garage distribution panel have egc and neutral seperate as required in each panel.

House panel is 125 AMP service. Stand alone garage panel is 100 AMP service.

I cannot find a code section on this.
Q - Can both these two distribution panels be bonded together (EGC and neutral) at the same location inside the Ronk manual transfer switch?
Q - If they can be does the 1st bond of neutral and ground at the outside service entrance disconnect (on the other side of the house) cause a problem by being a second EGC and neutral bond?

Thanks.

2017 / 2014 NEC & Related Books and Study Guides
Re: EGC Bond in Transfer Switch (Code) [Re: George393] #193638 04/11/10 11:50 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Your code reference is 250.32.

You can not tie the "Grounded" conductor to the equipment after the Service Disconnect. You must carry an equipment ground conductor with any feeders and keep the Grounded conductor (Neutral) and the equipment grounding conductor separated. If your generator is a SDS you must use a 3-pole transfer switch (assume single phase) and transfer the neutral.

By the way Welcome to the forum. With a name like George your okay.


George Little
Re: EGC Bond in Transfer Switch (Code) [Re: George Little] #193653 04/12/10 05:38 PM
Joined: Apr 2010
Posts: 5
G
George393 Offline OP
New Member
Thanks George!


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,641 Are you busy
209,564 Re: Forum
196,916 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3