EGC Bond in Transfer Switch (Code) #193637
04/12/10 12:17 AM
04/12/10 12:17 AM
G
George393  Offline OP
New Member
Joined: Apr 2010
Posts: 5
AL
A customer requests an addtional circuit (3 outlets) in a stand alone garage.

She has an outside 100 AMP disconnect at the entrance. From there the feeder goes direct to the oposite side of the house and terminates at a Ronk 100 AMP manual transfer switch (for a portable generator hookup).

EGC and all neutrals from the single house distribution panel and the stand alone garage distribution panel are bonded together inside the Ronk manual transfer switch. The house distribution panel and the stand alone garage distribution panel have egc and neutral seperate as required in each panel.

House panel is 125 AMP service. Stand alone garage panel is 100 AMP service.

I cannot find a code section on this.
Q - Can both these two distribution panels be bonded together (EGC and neutral) at the same location inside the Ronk manual transfer switch?
Q - If they can be does the 1st bond of neutral and ground at the outside service entrance disconnect (on the other side of the house) cause a problem by being a second EGC and neutral bond?

Thanks.

2017 / 2014 NEC & Related Books and Study Guides
Re: EGC Bond in Transfer Switch (Code) [Re: George393] #193638
04/12/10 12:50 AM
04/12/10 12:50 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Your code reference is 250.32.

You can not tie the "Grounded" conductor to the equipment after the Service Disconnect. You must carry an equipment ground conductor with any feeders and keep the Grounded conductor (Neutral) and the equipment grounding conductor separated. If your generator is a SDS you must use a 3-pole transfer switch (assume single phase) and transfer the neutral.

By the way Welcome to the forum. With a name like George your okay.


George Little
Re: EGC Bond in Transfer Switch (Code) [Re: George Little] #193653
04/12/10 06:38 PM
04/12/10 06:38 PM
G
George393  Offline OP
New Member
Joined: Apr 2010
Posts: 5
AL
Thanks George!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,370 Are you busy
190,634 Re: Forum
180,357 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 15 (0.004s) Memory: 0.9520 MB (Peak: 1.0756 MB) Zlib enabled. Server Time: 2019-04-18 10:39:23 UTC