30KVA dry type transformer (480 X 120/208)
Can it be located above a suspended accessible ceiling (say in a medical office building)?
Can it be located above this ceiling if the ceiling space is a return air plenum?

2017 / 2014 NEC & Related Books and Study Guides
Re: transformer above ceiling? [Re: cgw] #193502
04/05/10 06:10 PM
04/05/10 06:10 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
NEC 2008 450.13(B) says, generally for this size and type, you can. The plenum space question is not addressed.

Re: transformer above ceiling? [Re: Gregtaylor] #193506
04/05/10 08:40 PM
04/05/10 08:40 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,063
Brick, NJ USA
300.22 (c)(2) should be read, and then I suggest you speak to the local AHJ for his/her interp. Under 50 KVA is no issue, BUT...the air handling ceiling needs to be addressed. Also, you may want to have a cut sheet for the exact xfr you intend to install.



John
Re: transformer above ceiling? [Re: HotLine1] #193508
04/05/10 09:52 PM
04/05/10 09:52 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,335
Estero,Fl,usa
I think this is probably legal, depending on the transformer but it might be a questionable design choice. If that transformer smokes it will share the joy with the rest of the building pretty fast, at least that HVAC zone anyway.


Greg Fretwell
Re: transformer above ceiling? [Re: gfretwell] #193588
04/08/10 07:07 PM
04/08/10 07:07 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
If the Life Safety System ( Fire Alarm ) is up to snuff a duct detector is going to shut things down well enough in time.

Not quite the same set-up...

But I rigged a 45kVA XFRMR, dry-type, above a grid to give isolated power to data loads. Upon the detection of fire, within this space only, a shunt-trip killed total power - with a time delay of seconds so that the data state could be frozen/ preserved. Subsequently the dry fire system would be flooded into the now unpowered space.

So the question of plenum return air really would seem to be a life safety question not to be answered within our Code.


Tesla

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
Popular Topics(Views)
252,839 Are you busy
189,628 Re: Forum
179,294 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.005s) Memory: 0.9684 MB (Peak: 1.1085 MB) Zlib enabled. Server Time: 2019-01-24 00:48:01 UTC