#193031 03/16/10 02:55 PM
Joined: Oct 2001
Posts: 81
G
Member
First off let me say it has been over 15 years since I was involved in anything using conventional electrical components in Canada and maybe 20 years since I was ever asked anything to do with Health Care Facitlies in Canada.
In the US there is cable specified for Health Care (AC-HFC) and for non Heath care MC is used. Now there is a crossover between the two. In Canada I had the impression normally for normal 120 receptalces we would use the hospital grade receptacle and 12/2 BX with insulated ground is this correct or am I in need of a refesher on Canadain Standards?

Joined: Jun 2006
Posts: 613
M
Member
It depends.
The use of armoured cable requires approval from the local authority. IE special permission.
Locally that is very easy to get. The bonding conductor is required to be insulated against accidental contact with the armour if you are using armoured cable (BX) or (AC)
Typically that is ISO (isolated) the construction of ISO bx is insulated power conductors and 1 insulated bonding conductor as well as a bare. Regular AC cable is not permitted as the bonding wires are bare and it is not a #12 as is the minimum size for the insulated bonding wire.
Teck cable sized for the minimum #12 bonding wire is acceptable and in combustible buildings we even permit 10-2 loomex as the bonding wire is #12. Clearly the voltage drop and potential rise test have to be passed and the results submitted to the inspection department.
If you are doing a real hospital as opposed to a GP's office you will be using pipe and wire.

Joined: Oct 2001
Posts: 81
G
Member
Thanks


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Top Posters(30 Days)
dsk 5
Popular Topics(Views)
284,568 Are you busy
217,279 Re: Forum
203,631 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5