Wall Packs
#192839
03/05/10 09:43 PM
|
Joined: Jul 2002
Posts: 241
OP
Member
|
Does the code allow you to run a conduit from the side of a Wall Mounted Metal Halide fixture(Wall Pack), if an existing feed runs into the back of the fixture? Would the fixture then be a raceway? I may go a different route and not pick my feed for a new light off of an existing wall mount fixture. TGIF
|
|
|
Re: Wall Packs
[Re: SJT]
#192841
03/05/10 10:15 PM
|
Joined: Nov 2007
Posts: 763
Member
|
410.65 in the '08 NEC specifically allows luminaires to be connected together that way. It also states that the fixture is not required to be listed as a raceway for this purpose.
|
|
|
Re: Wall Packs
[Re: KJay]
#192846
03/06/10 02:32 PM
|
Joined: Apr 2002
Posts: 7,235
Member
|
I agree with KJay. I don't believe there have been any changes from previous NEC (2005-2002, etc)
John
|
|
|
Re: Wall Packs
[Re: HotLine1]
#192851
03/06/10 11:52 PM
|
Joined: Feb 2008
Posts: 165
Member
|
This is the easy way to add a fixture to an existing building
|
|
|
Re: Wall Packs
[Re: Rewire]
#192853
03/07/10 12:09 AM
|
Joined: Jul 2002
Posts: 241
OP
Member
|
Thanks for the replies. When we install the 3 new lights, we may be replacing the wall pack with a weather-proof round box. The 3 new lights may shine enough light.
|
|
|
|
|