Here's an oddity I came across. An electrician was called to a house, because of lights flickering. He came to believe there was an open in the neutral of a 2-wire branch circuit. But he was unable to locate and correct the open. So, he jumpered the neutral to the neutral of another 2-wire branch circuit, in an existing outlet box.

Which sections of the NEC did he violate?


Horizontal Ad
Joined: Jul 2004
Posts: 10,026
Likes: 37
G
Member
300.3(B)? 310.4?


Greg Fretwell
Joined: Mar 2003
Posts: 849
Y
Member
I'd agree with you 300.3(B).

Joined: Feb 2008
Posts: 165
R
Member
210.4 (B)

Joined: Mar 2003
Posts: 849
Y
Member
210.4(B) is for ungrounded conductors not grounded conductors.

Joined: Feb 2008
Posts: 165
R
Member
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.

Joined: Nov 2002
Posts: 793
Likes: 3
W
Member
I don't know the code, especially chapter and verse, but I think you'd have 4 bad results: a) depending on the phasing of the other circuit, if it happens to be the same phase you could get an overloaded neutral, b) Violation of that code rule saying "no paralleled wires (except for a few well restricted exceptions)", and c)the other circuit's breaker needs to be ganged with the first circuit's breaker. And you'd have current passing thru the hot wire of one cable (raceway) and returning thru a separate cable (raceway) neutral wire (because of an open on the first raceway's neutral) which I'm sure is a 4th violation and if not, still undesirable. You'd have a large loop of 60Hz magnetic activity happening, and in severe enough cases you could get magnetic inductive heating of connector and box hardware.

Horizontal Ad
Joined: Feb 2008
Posts: 165
R
Member
300.3 B(4) allows seperate cables as long as you comply with 300.20 B

Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Rewire:

Originally Posted by Rewire
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.


John
Joined: Feb 2008
Posts: 165
R
Member
Originally Posted by HotLine1
Rewire:

Originally Posted by Rewire
Originally Posted by Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
The OP needs clarity, a branch circuit by definition has 2 conductors so stating it was a 2 wire branch circuit was a bit misleading I made the assumption he was speaking of a MWBC either way a handle tie breaker would be required a simple voltage check at the box would tell you if you were on the same phase.

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 34
Joined: June 2004
Top Posters(30 Days)
Popular Topics(Views)
554,272 Are you busy
428,583 Re: Forum
398,651 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5