0 members (), 526 guests, and 26 robots.
#192671 02/23/10 02:01 AM
MJ2000 Offline OP
Hi guys,
I need an explanation for the ESA09 Rule 02-034.
Thanks
MJ2000 #192673 02/23/10 01:56 PM
Don't throw an electric fan into a bathtub in an attempt to create a jaccuzi.
brsele #192674 02/23/10 02:27 PM
Not sure what your getting confused on? I agree with brsele. You could also say Rule 2-034 means not to use steel conduit as a replacement for copper conductors!!!
Never trust an electrician with no eyebrows!!
MJ2000 Offline OP
I didn't post this topic as a joke. I couldn't find this rule in the Code book.The problem is that I got this in the Notice of Deficiency from an inspector and an explanation for this rule is "Panel covers shall be installed.
MJ2000 #192678 02/23/10 08:58 PM
were panel covers missing ?? you really have not explained much here.
I am in BC and that rule is not in the CEC. what does it say in the ESA
dougwells #192679 02/23/10 09:09 PM
2-034 Use of approved equipment
No person shall use electrical equipment for any purpose or in any manner other than the purpose or manner for which it is intended.
Thanks smile
dougwells #192684 02/24/10 02:58 PM
If the inspector said panel covers shal be installed i would think he might quote 2-202 or other rule from 2-200.
Cover on or off, i am assuming the panel was being used as a panel?
mikesh #192687 02/25/10 12:30 AM
MJ2000 Offline OP
* Two screws missing from the panel cover
It could be reason for that notice, but it has been for long time!
