ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Recent Posts
Chinese motors rated 220 v 50 hertz
by gfretwell - 07/23/24 04:45 PM
100 Definitions: Accessible 2023
by gfretwell - 07/23/24 10:12 AM
100 Definitions, Likely to Become Energized, 2023
by gfretwell - 07/23/24 10:08 AM
240V only in a home and NEC?
by emolatur - 07/18/24 01:05 PM
2023 CEU Course
by gfretwell - 07/17/24 01:08 AM
Advertisement:-Left
Recent Gallery Topics:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (InspE), 437 guests, and 32 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#192665 02/22/10 04:01 PM
Joined: May 2001
Posts: 378
F
frank Offline OP
Member
They have a 50amp breaker and ran #6 up into a box spliced it with split bolts to #4 teck cable for the length of run then into another box spliced it again to a #6 for a drop to a machine.I know you can run #4 to #6 as long as the breaker is sized for #6 but doing it at both ends seems just plain wrong since Ive never seen this done before with ten yrs in the trade.They also used BX connectors instead teck connectors???Someone else did the work and they want me to terminate it.I will be inspected and they say i will pass but i don't think so.
opinions please
thanks

Horizontal Ad
Joined: Sep 2006
Posts: 111
E
Member
I don't see a prob with the wire sizing.
Only need the teck connectors if it's outside or in a damp location. Had this come up recently where one inspector said yes, the other said no. Final answer was that if it's inside you treat it like bx. Just strip back enough of the outer casing so the connector is in contact with the metal sheath.

Joined: Jun 2006
Posts: 613
M
Member
First teck connectors are required for wet locations or hazardous locations. Flex and BX connectors are approved for dry locations for teck assuming condition 1 and 2 do not exist. The biggest challenge with many of the dry connectors is that they do not tighten up to the armour thus neither a good mechanical or electrical connection.
Now #4 to #6. as long as the wire is that size for voltage drop and the OC protection is for #6 then great. Maybe the largest lugs in the supply and load would not accomodate #4 wires. I saw a job that sized all the home runs for %3 volt drop and a few receptacle runs used #6 which were spliced down to #12 for connection to breakers and receptacles. I think that job was designed by some guy that just took a harmonics and volt drop seminar. They might even recoup the added expense over a hundred years on line loss savings ;-) By the way it was an OSH (Worksafe) office in Vicoria BC.

Joined: May 2001
Posts: 378
F
frank Offline OP
Member
EddyCurrent,mikesh
Ok thanks for the replies



Link Copied to Clipboard
Advertisement:-Right

* * * * * * *
Tools for Electricians
Tools for Electricians
 
* * * * * * *

2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
323,575 Are you busy
247,890 Re: Forum
231,670 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5