Spec for AL to Copper Splice Block #191731 01/09/10 04:53 PM
Joined: Jan 2010
Posts: 2
Y
YoLektrician Offline OP
New Member
Hi, I am looking for a spec recommendation on a insulated ( non compression) splice block that is rated for Aluminum to Copper Connections for typical Risers. The intornetz is giving me a tumor trying to find a suitable device. I am basically looking to extend a old 3 Wire Aluminum Feeder. Splice will be made inside a JB where the old panel was.

Any input is appreciated.

Work Gear for Electricians and the Trades
Re: Spec for AL to Copper Splice Block [Re: YoLektrician] #191732 01/09/10 05:14 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I would think that any Polaris / NSI connector would work for wires over #8.

Re: Spec for AL to Copper Splice Block [Re: renosteinke] #191733 01/09/10 07:45 PM
Joined: Nov 2006
Posts: 23
W
wire twister Offline
Member
Polaris connector would be my choice.

Re: Spec for AL to Copper Splice Block [Re: wire twister] #191736 01/10/10 07:23 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
I pretty much the same pages as two guys mention above get Polaris connector they are pretty easy to use it and there is few verison you can use depending on which way you run the conductors in the Jbox.

A reminder here becarefull with sizing the junction box don't get too small a jbox.

Merci,Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Spec for AL to Copper Splice Block [Re: YoLektrician] #191759 01/11/10 01:23 PM
Joined: Jan 2010
Posts: 2
Y
YoLektrician Offline OP
New Member
Thanks for the responses


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Admin 8
Popular Topics(Views)
278,839 Are you busy
211,999 Re: Forum
199,039 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3