mother-in-law apartment #190657
11/29/09 03:16 AM
11/29/09 03:16 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I have royally blundered my service design for this house with a mother-in-law apartment(I think?... in some fairness to myself, I am picking up where someone else left off). I have a remote 400 amp service on a well house 100 feet away from main house. I ran underground wires to house, and I went into an LB and then into a JBox which I used tap blocks to splice SER cable to the underground wire(without a disconnect-mistake #1)which feeds main house panel.Then from that panel I am feeding the mother-in-law apartment 100 amp sub-panel with main back feed breaker(mistake #2?) I realize now I need a 200 amp disco for SER cable that feeds house panel, and want to place it inside the house at closet point of entry, but that is a closet. Can I stick my disco in coat closet? And if I did would I get bit by 225.35 access for mother-in-law occupant? Which is my second question "Should I just get a rain tight disco and place outside meeting 225.32 and 225.35 in one fail swoop?"

This is my first experience in twenty years with this type of remote service and I am paying a hefty price!!

Thanks guys,
H20

Last edited by watersparkfalls; 11/29/09 03:21 AM.
2017 / 2014 NEC & Related Books and Study Guides
Re: mother-in-law apartment [Re: watersparkfalls] #190658
11/29/09 03:43 AM
11/29/09 03:43 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I am wondering if the main breaker at twin meter(main service)qualifies as access to supply for occupants?

Re: mother-in-law apartment [Re: watersparkfalls] #190676
11/29/09 10:44 PM
11/29/09 10:44 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I personally wouldn't install it in a clothes closet anyway, but if the disconnect contains overcurrent protection, I would definitely say it's a no-go, at least per 240.24[D].
IMO, an outdoor disconnect located at grade level in a common area would meet the requirements of both 230.70[A],1, Readily Accessible Location and 230.72, Access to Occupants.

Re: mother-in-law apartment [Re: KJay] #190682
11/30/09 11:35 AM
11/30/09 11:35 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
Thanks Kjay,
trying to stretch clothes to coat...
But ignitable covers both.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
BigB 3
Popular Topics(Views)
252,787 Are you busy
189,594 Re: Forum
179,262 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 15 (0.004s) Memory: 0.9601 MB (Peak: 1.0924 MB) Zlib enabled. Server Time: 2019-01-21 12:30:04 UTC