240 tap rules #190599 11/25/09 11:12 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
I have a question about taps not over 25 foot.

Scenario:
I have a 320 amp service w/twin meter outside a well house with 2-200 amp Main breakers(established service). One breaker feeds the shop and the other feeds the house and the well house. Here in the meter base on the customer side I used tap blocks to w/4/O AL to feed 200 amp panel in house and 1/O AL to feed 100 amp panel(12 feet from meter base) in the well house and 4/O from main breaker to a 3 hole tap block in meter base. Originally I came from back of meter base with 1/O SER cable and fed 100 amp panel inside well house(not in a raceway)this cable was inside the wall of well house and above in trusses, which is going to be finished with drywall. Is physical damage applied to cables in a wall? I read the not over 25 foot rule as not specifically requiring a raceway as written in 10 foot rule or over 25 foot rule. Am I reading to deep into other approved means? To pass my inspection I changed SER cable to underground direct burial wire and ran outside the well house to panel, using the outside tap rules.
Thanks Guys and Happy Turkey Day!!!
H2O

2017 / 2014 NEC & Related Books and Study Guides
Re: 240 tap rules [Re: watersparkfalls] #190653 11/29/09 12:12 AM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
Not sure I'm following the question completely, but 240.21,[2] in the '08 NEC states as a requirement that "The tap conductors are protected from physical damage by being enclosed in an approved raceway or by other approved means".
This is also mentioned as one of the requirements in 240.21,[4] Taps Over 25 Feet Long.

IMO, I think an approved raceway is easy enough to comply with, but as far as what "other approved means" would be... that sounds like it is going to be up to the actual AHJ to decide.

Re: 240 tap rules [Re: KJay] #190661 11/29/09 10:45 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I think you have to read between the lines a bit.

For example ... bus duct. Is it enclosed? Is it a receway? Or, perhaps, is it a specialty product, designed specifically for this use?

Re: 240 tap rules [Re: renosteinke] #190671 11/29/09 08:05 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
IMO, I'd say that busway is both a raceway, as defined in Art.100, as well as an enclosure as described in 368, but I think the question remains... is it approved for this installation, since it cannot be used where exposed to "severe physical damage", a term which also appears to not be clearly defined. Another question to the AHJ?

Re: 240 tap rules [Re: KJay] #190672 11/29/09 09:04 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
It's simply not possible to write any set of rules that covers each and every possible situation over an endless period of time - if for no other reason than the limits of language.

That's why the "master's" get the respect, and why the AHJ is not some committee meeting in a hotel room someplace.

Forget the techno-babble. All anyone can do is be prepared to persuade twelve of their neighbors that they made the right call.

Re: 240 tap rules [Re: renosteinke] #190673 11/29/09 10:20 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
I suppose Reno, but I think in the OP's case, the first step should be to at least pass inspection before he moves on to a trial by jury. smile From what I can gather, it sounds like maybe heís already had to rework the installation once already.

Iím also assuming that his inspector most likely has access to information available from the AHJ to assist with his interpretations as to what is acceptable, but donít know for sure, so maybe not.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,437 Are you busy
209,330 Re: Forum
196,614 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3