ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#190025 11/03/09 05:05 PM
Joined: Mar 2003
Posts: 849
Y
Member
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2005
Posts: 1,213
S
Member
Originally Posted by Yoopersup
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup
If it's a delta generator, I hope it's a delta pump. If it's a delta pump, you don't need a neutral. 250.24(C) doesn't apply to delta panels, as the AC system is not grounded at any point.

Easy answer: don't run the neutral.

Joined: Mar 2003
Posts: 849
Y
Member
480/277 Volt System at both Generator & Service Thus Neutral required per 250.24c to ist disconnect switch per code.Since Feeder Neutral is not required only equipment gr. But Service requires Neutral.
Yoopersup