#190025 - 11/03/09 05:05 PM Fire Pumps 695  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup


2017 / 2014 NEC & Related Books and Study Guides

#190054 - 11/04/09 03:04 PM Re: Fire Pumps 695 [Re: Yoopersup]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,208
Chesapeake, VA
Originally Posted by Yoopersup
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup
If it's a delta generator, I hope it's a delta pump. If it's a delta pump, you don't need a neutral. 250.24(C) doesn't apply to delta panels, as the AC system is not grounded at any point.

Easy answer: don't run the neutral.


#190058 - 11/04/09 04:39 PM Re: Fire Pumps 695 [Re: SteveFehr]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
480/277 Volt System at both Generator & Service Thus Neutral required per 250.24c to ist disconnect switch per code.Since Feeder Neutral is not required only equipment gr. But Service requires Neutral.
Yoopersup



Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7526 MB (Peak: 0.8745 MB) Zlib enabled. Server Time: 2017-08-18 01:21:03 UTC