Fire Pumps 695 #190025
11/03/09 05:05 PM
11/03/09 05:05 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup

2017 / 2014 NEC & Related Books and Study Guides
Re: Fire Pumps 695 [Re: Yoopersup] #190054
11/04/09 03:04 PM
11/04/09 03:04 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by Yoopersup
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup
If it's a delta generator, I hope it's a delta pump. If it's a delta pump, you don't need a neutral. 250.24(C) doesn't apply to delta panels, as the AC system is not grounded at any point.

Easy answer: don't run the neutral.

Re: Fire Pumps 695 [Re: SteveFehr] #190058
11/04/09 04:39 PM
11/04/09 04:39 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
480/277 Volt System at both Generator & Service Thus Neutral required per 250.24c to ist disconnect switch per code.Since Feeder Neutral is not required only equipment gr. But Service requires Neutral.
Yoopersup


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,538 Are you busy
190,772 Re: Forum
180,494 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.9516 MB (Peak: 1.0746 MB) Zlib enabled. Server Time: 2019-04-23 04:14:11 UTC