Can some one explain what is Redundant grounding

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
The term is used in article 517 (patient care areas) it generally refers to an additional grounding conductor.
They require a properly made up metallic wiring method (your ground) plus an insulated grounding wire (the redundant ground).

Joined: Oct 2009
Posts: 3
M
New Member
Keep in mind the first EGC can be your conduit, then a properly sized insulated EGC inside.