GFCI-680.22(B) FlA? #189275
09/28/09 09:51 PM
09/28/09 09:51 PM
L
leland  Offline OP
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
http://www.nema.org/stds/fieldreps/codealerts/20090928fl.cfm

Does this mean that 1 & 2 family dwellings don't need GFCI protection on their pools?


Section 2705 Equipotential Bonding GFCI Protection



2705.1 NFPA 70 - 08: National Electric Code, Article 680 (Swimming Pools, Fountains, and Similar Installation), Section 680.22(B), GFCI Protection, is amended to read as follows:



(B) GFCI Protection. Outlets supplying pool pump motors from branch circuits with short-circuit and ground-fault protection rated 15 or 20 amperes, 125 volt or 240 volt, single phase, whether by receptacle or direct connection, shall be provided with ground-fault circuit-interrupter protection for personnel.



Exception: One-and two-family dwellings.

2017 / 2014 NEC & Related Books and Study Guides
Re: GFCI-680.22(B) FlA? [Re: leland] #189276
09/28/09 10:27 PM
09/28/09 10:27 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,036
Brick, NJ USA
Talk about 'doublespeak'!

Greg....what say you??


John
Re: GFCI-680.22(B) FlA? [Re: HotLine1] #189277
09/28/09 10:33 PM
09/28/09 10:33 PM
L
leland  Offline OP
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Glad it aint just me. I had that "puppy want a treat" look on my face when I read it.

Re: GFCI-680.22(B) FlA? [Re: leland] #189280
09/29/09 12:22 AM
09/29/09 12:22 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Florida exempted hard wired pool pumps in 1 & 2 family, at least that is what the intent was. It does look like the wording they came up with completely removed the GFCI requirement for hardwired and 240v pumps. 120v 15-20a Receptacles "outdoors" will still need GFCI protection.
I suppose an indoor pool wouldn't need any GFCIs
There are plenty of inspectors who disagreed with this change.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,596 Are you busy
188,120 Re: Forum
177,778 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 0.9604 MB (Peak: 1.0921 MB) Zlib enabled. Server Time: 2018-10-22 10:00:41 UTC