Joined: Jul 2004
Posts: 9,745
Likes: 13
G
Member
I see there is no more "lighting and appliance" panelboard in the 2008 so I suppose the defacto 2 breaker disconnect limit is gone too.
Is this saying you can put a 6 breaker panel in the detached garage without any other means of disconnect? (assuming it is adequately protected at the house)


Greg Fretwell
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jan 2005
Posts: 5,349
Likes: 1
Cat Servant
Member
I'm not sure I know what '2 breaker' limit you're referring to. Nor do I see how the '6 disconnect' rule aplies.

The 'six throws of the hand' rule applies to services, not to 'sub' panels. You have that panel protected by just one disconnecting /OCPD means, though that can be at either end of the feeder, or any place inbetween.

What that little change in vocabulary means is that the 42 breaker limitation is gone, as are all the arguments over whether something is a 'poer' or 'lighting' panel. That panel can have a gazillion breakers in it, and it doesn't matter how many of the circuits need neutrals.

Joined: Jul 2004
Posts: 9,745
Likes: 13
G
Member
There used to be a rule that said a lighting and appliance panelboard had to be protected by 1 or 2 main breakers. AHJs read that to mean if you had a sub panel in a detached building with 6 breakers you needed a main breaker so the 6 disconnect rule was moot.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 812
Joined: April 2004
Top Posters(30 Days)
Jim M 5
Trumpy 4
Popular Topics(Views)
297,348 Are you busy
228,231 Re: Forum
213,133 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5