#189134 09/21/09 03:10 PM
Joined: Feb 2002
Posts: 2,233
H
Member
Here is a question. There is a deck box to a pool. It is the newer style (Intermatic is the manufacture) where you can install 2-3 pipes to the deck box. Each PVC pipe to the deck box has a # 8 cu wire from the wet niche to the proper ground strip inside the deck box. It also has the required #12 CU ground wire back to the pool control box. The deck box is installed properly. ( Height of ground, distance from pool, etc.)

This particular deck box happens to have an external bonding lug. The manufacture instruction state, "The external grounding lug is provide in case your installation requires it."

Now the question, if everything is wired properly, as per the 2005 or 2008 NEC, would you need to use that bonding lug? When would that external ground lug be needed? Should there be a # 8 CU bond wire back to the pool control box? Should that external ground lug need to be connected to the bonding grid? Should nothing be hooked to that external lug?

Any thoughts? Thanks

Horizontal Ad
Joined: Apr 2002
Posts: 7,411
Likes: 7
Member
Harold:
I did a quick look at Intermatic's website & see nothing about any deck boxes.

I assume the box you reference is plastic. The only logical guess I have is perhaps a tie-in to the 680.26 bonding?



John
HotLine1 #189140 09/21/09 05:49 PM
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
Quote
perhaps a tie-in to the 680.26 bonding?


That is what I did with mine although the #8 stranded from the niche (2 in my case) is also part of the 680.26 grid. It was just easy because I had the #8 solid going right by the J box on the way to the pump, heater pad. I figure the more bonding the better in a pool.


Greg Fretwell
gfretwell #189156 09/22/09 11:48 AM
Joined: Feb 2002
Posts: 2,233
H
Member
Let's see if I can do this right. I will try to copy the web page of the box I am looking at.

http://www.intermatic.com/~/media/files/intermatic/catalog/pages/141.ashx

Go to that page and see if it works. It is a deck box with an external grounding/bonding lug. There is discussion as to see if it would be required or is it an option to connect to this lug.

The deck box has an internal #8 which does connect to the #12 cu wire frond the pool light.

Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
I can't think of anything that is required to be connected to that lug. You need the hot, neutral and insulated EGC from the line side, the hot, neutral and EGC to the light via the cord and the #8 bonding conductor from the niche.
The niche also gets bonded to pool steel.
These days the niche is usually plastic so all you are really bonding is the speed nut that the light screws into


Greg Fretwell
gfretwell #189176 09/22/09 10:36 PM
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

At first I thought that you should bond to that lug, but the more I think about it and ask others, the more I guess that it does not have to be bonded to anything. I guess you could use that lug and bond to a fence if you were close enough to the fence.

Normally the contractor wouldn't have a problem coming back to throw a bond wire to the deck box. In this case the contractor is an hour away from the job. As long as the job is safe and meets code and manufactures instructions, then I would be OK with it.

Joined: Apr 2002
Posts: 7,411
Likes: 7
Member
Harold:
FWIW, & IMHO the external bond point is an access for any bonding, and not required to be connected as long as other bonding is intact.

Second thought....
Possible bonding for the niche, IF it's not tied in; like if it is stubbed-up adjacent to the PVC from the light??

BTW, thanks for that link...I just printed it for file reference & sharing.


Last edited by HotLine1; 09/23/09 09:21 AM.

John
Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
Popular Topics(Views)
347,089 Are you busy
272,200 Re: Forum
252,559 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5