ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
#188758 08/31/09 01:12 PM
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
Are aluminum conductors allowed for all feeders and branch circuits? Code sections? If someone can guide me to a previous thread on this, that would work too. Thanks.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Technically, as the code is written, there's no reason not to use aluminum for nearly everything. True, there are a few exceptions, such as certain grounding conductors where the NEC specifies theat aluminum shall NOT be used, but those are the exceptions.

Indeed, the aluminum wire makes will tell you that aluminum is every bit as reliable as copper.

Yea, right. The wire makers leave out a few details:

They neglect to mention the change they made in the alloy used in the late 70's, to address issues that - they still claim - were caused by poor installation.

They also neglect to point out that they don't make the stuff smaller than #6 anymore. So, while there's no rule against using all aluminum to wire a house, lots of luck finding that #12 Romex in aluminum.

The same paradox exists as to the use of anti-oxidant compounds. The wire makers say there is no more, or less, reason to coat aluminum than there is copper. The NECA standard seems to assume that you will use it when working with aluminum, but doesn't specifically tell you to use it. The NEC is silent on the issue.

This is -yet again - where 'trade practice' varies from what the rule books say. Personally, I'll stick with tradition.

Joined: May 2005
Posts: 984
Likes: 1
G
Member
Check with the local AHJ as to the minimum sizes allowed.
Most of them have no problems with Aluminum feeders but do have a cutoff size that they won't allow to be anything but Copper.
Around here, it's usually 10AWG and smaller, but it pays to check it out.


Ghost307
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
So where/how does 110.5 apply?

Joined: Mar 2008
Posts: 27
G
Member
PLEASE, please, please don't tie copper and alu together under a wire nut, even if "they" say that the nut is made specifically for that purpose.


Sometimes not getting what you want can be an incredible stroke of luck.
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Originally Posted by gpsparky
PLEASE, please, please don't tie copper and alu together under a wire nut, even if "they" say that the nut is made specifically for that purpose.


Who are the "they" you're talking about? Do you know something that UL doesn't or have you fallen for the scare tactics on one of the web pages that I swear is funded by the makers of the copalum splices?

The only drawback I can see to the wirenut that is listed for copper to aluminum is its large size, hard to jam back in those undersized boxes they use in the old mobile homes.

Last edited by Tom; 09/03/09 09:22 PM. Reason: duplicate word

Few things are harder to put up with than the annoyance of a good example.
Tom #188809 09/04/09 02:41 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Originally Posted by Tom


Who are the "they" you're talking about? Do you know something that UL doesn't or have you fallen for the scare tactics on one of the web pages that I swear is funded by the makers of the copalum splices?

Personally Tom,
There is absolutely no way that I would EVER put an aluminium wire and a copper wire in the same termination and call it "safe".

Sure the copper wire might be fine, but screwing a wirenut over an aluminium wire, is just asking for trouble.

These sorts of connections depend on friction only, not the sort of thing you want to subject aluminium to, as it has the habit of "flowing" under mechanical stress.

Especially when these connections are also carrying current, which will heat any sub-standard connection up, possibly to the melting point of the metal.

Bi-metallic lugs and splices are there to be used for a reason, otherwise, we wouldn't have them.

Joined: Mar 2005
Posts: 1,803
Member
UL= Underwriters Laboratories. The clue is in the name. If a product is approved, then it must have passed their tests, surely?


Wood work but can't!
Joined: Nov 2007
Posts: 764
K
Member
Not sure if this relates to the OP's question or not, but the thing I find a little unnerving about the Ideal purple wirenuts, is that the manufacturer has multiple warnings on the package that they are designed only for connecting aluminum-to-aluminum conductors with another copper conductor present, but not for straight aluminum to aluminum only.
Not sure about the T&B Marette ACS wirenut though, but according to the T&B product literature, they are not even UL Listed, so not sure how you could actually use them.
If I need to splice small AWG aluminum to aluminum or aluminum to copper, which thankfully is a rare occurrence for me, I use the AlumiConn set screw type connectors and a torque screwdriver, so as to make it a UL Listed splice. These still can take up a lot of room in a box, but IMO they are presently the next best alternative to the actual Copalum splices

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
One thing a lot of people seem to ignore is that most lugs are aluminum. It would seem (as Alcan, among others will say) aluminum wire performs better in these lugs than copper.


Greg Fretwell