Common wall resi boxes #188072
07/20/09 10:19 PM
07/20/09 10:19 PM
D
derater  Offline OP
Member
Joined: Mar 2002
Posts: 179
I'm roughing in a row of townhomes. The adjoining walls are separate; 2- 2x4 walls. Is there any special requirement for the device boxes on these walls p/2005 NEC? Thanks.

Work Gear for Electricians and the Trades
Re: Common wall resi boxes [Re: derater] #188074
07/20/09 11:13 PM
07/20/09 11:13 PM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,334
Alaska
That will be in the local building code requirements. The IBC for example requires a minimum of 24" or solid fire blocking i.e., framings studs.


"Live Awesome!" - Kevin Carosa
Re: Common wall resi boxes [Re: sparkyinak] #188077
07/20/09 11:43 PM
07/20/09 11:43 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Derater:

There's a lot of info that you may need:

Is sheetrock going in the cavity between the two 2x4 walls? How about core wall board? It would have to go thru continuous. IF that's the case, you are in regular walls, as long as you don't penetrate thru.

IF there is nothing between the two walls:
Openings on both sides of fire rated wall must be 24" apart. Hilti makes a 'putty pad' (firestoping) that can be wrapped around boxes that are closer but it's $$$

This applies to ALL openings, electric, phone, cable, HVAC, etc.

Also, be careful for a rated ceiling with penetrations.

Your best bet is to check with the Building Inspector before you start to save what could be a lot of grief.



John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,123 Are you busy
185,581 Re: Forum
174,903 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.005s) Memory: 0.9514 MB (Peak: 1.0775 MB) Zlib enabled. Server Time: 2018-07-19 06:09:19 UTC