Ice machine conduit 'repair' #187872
07/13/09 12:09 AM
07/13/09 12:09 AM
B
Bigplanz  Offline OP
Member
Joined: Mar 2009
Posts: 73
Louisville, Kentucky
At my local CVS their ice machine is outside by the door. No GFCI on the outlet I guess (didn't test it) but what caught my eye was this 'repair' of a piece of broken PVC conduit. Doubt it is 'water tight.' smile


Attached Files IMG_0002.jpg
2017 / 2014 NEC & Related Books and Study Guides
Re: Ice machine conduit 'repair' [Re: Bigplanz] #188045
07/19/09 12:37 AM
07/19/09 12:37 AM
JoeKP  Offline
Member
Joined: Mar 2008
Posts: 144
Berkley, MA
HAHA, nice, it looks kind offset, was there some kind of pull box there before the duct tape took over??


-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH
Re: Ice machine conduit 'repair' [Re: JoeKP] #188075
07/20/09 10:31 PM
07/20/09 10:31 PM
B
Bigplanz  Offline OP
Member
Joined: Mar 2009
Posts: 73
Louisville, Kentucky
The power was from above, and there was a box that the line came out of. I reported this to property maintenance which flagged it as 'low priority.' smile


Re: Ice machine conduit 'repair' [Re: Bigplanz] #188094
07/21/09 01:39 PM
07/21/09 01:39 PM
Theelectrikid  Offline
Member
Joined: Apr 2004
Posts: 810
Levittown, PA
Looks like the CVS by Five Points, usually after they do their weekly repair of their brick wall car damage.

Ian A.


Is there anyone on board who knows how to fly a plane?
Re: Ice machine conduit 'repair' [Re: Theelectrikid] #188110
07/21/09 09:53 PM
07/21/09 09:53 PM
B
Bigplanz  Offline OP
Member
Joined: Mar 2009
Posts: 73
Louisville, Kentucky
I think EMT or rigid would have been a better choice. Here you can see the carts and cars run straight into the PVC conduit. You can see the broken splice right above where the cart is leaning on the conduit. PVC is ok, but not in an application like this.

[Linked Image]

Re: Ice machine conduit 'repair' [Re: Bigplanz] #188111
07/21/09 10:44 PM
07/21/09 10:44 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
This illustrates one of the 'unenforceable' parts of the NEC.

110.3(A)(1) states that in judging an installation, 'suitavility' shall be considered. Too often, this is limited to looking for a UL lable. That's a mistake, in part because (2) goes on to address the 'adequacy' of the protection. (8), at the end of 110.3, even has a 'catch-all' provision allowing for the consideration of 'other factors.'

110.12(B) addresses the integrety of equipment, saying that there shall be no damaged parts that may affect safe operation.

The second part of the puzzle was that inspections happen only in response to a permit at the time of installation. There seems to be no provision for anyone to act afterwards - even when the failings are not only obvious, they are in a public place (and thus there is no expectation of privacy).

Were I to be asked to repair such an installation, I would consider it a requirement to take the impact of shopping carts into account with my repair. If that meant adding a guard, additional supports, or even changing the wiring method, I would do so. Simply replacing one failed system with another inadequate one does not, IMO, meet your code obligations.

Re: Ice machine conduit 'repair' [Re: renosteinke] #188116
07/22/09 08:04 AM
07/22/09 08:04 AM
B
Bigplanz  Offline OP
Member
Joined: Mar 2009
Posts: 73
Louisville, Kentucky
This installation has multiple issues. The receptacle with no cover, being another. I doubt they got a permit for this. I can't see this passing an inspection.


[Linked Image]

Re: Ice machine conduit 'repair' [Re: Bigplanz] #188148
07/23/09 03:06 AM
07/23/09 03:06 AM
TOOL_5150  Offline
Member
Joined: Aug 2007
Posts: 61
Bay Area
At least they used tapcons.

~Matt


I would rather beg for forgiveness then beg for permission.
Re: Ice machine conduit 'repair' [Re: TOOL_5150] #188151
07/23/09 08:47 AM
07/23/09 08:47 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
Weatherproof while in use covers (bubble covers) have mixed survival rates. I would have an issue with the one in the pic, as to it's orientation,

That said, once an inspection is completed and approved, I have no 'legal' jurisdiction. The issue falls under 'property maintenance' in a lot of localities. However, situations similar to the pic result in a phone call to the uniformed fire dept inspector, as he/she can write it up as a safety item, and also write $$$ violations if it is ignored.



John
Re: Ice machine conduit 'repair' [Re: HotLine1] #188351
08/01/09 07:58 PM
08/01/09 07:58 PM
M
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
Re the outlet, a bubble cover would have broken just as fast as the PVC flip lid cover that they used. A better solution is to hide the plug behind the machine.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,513 Are you busy
188,688 Re: Forum
178,391 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.073s Queries: 17 (0.030s) Memory: 1.0276 MB (Peak: 1.2130 MB) Zlib enabled. Server Time: 2018-11-16 20:14:01 UTC