Which Cartridge Fuse?
#187496
06/28/09 10:29 PM
|
Joined: May 2004
Posts: 24
OP
Member
|
I have an old family farm house with a 125 amp Square D breaker box. The service disconnect is a 100 amp Square D cartridge fuse. I have never had the main blow, but I decided that I better have a spare pair of fuses on hand just in case, as in this rural area it would be difficult to locate one in a hurry. I drove to the nearest city and located fuses at Lowes, but I am not sure which one of the two types they had should be used for my application. The heavy-duty time-delay one said it is "for motor and main panel protection. (FRN-R)" It indicated that "for lighting or electric heating circuits use general purpose fuses.(NON)" I use window AC units for cooling, and 1500 watt portable heaters for infrequent use in winter heating. Water heaters are also electric. (This is generally just a week-end house.) Which type of fuse would be the most appropriate for my use?
|
|
|
Re: Which Cartridge Fuse?
[Re: thiggy]
#187497
06/29/09 12:41 AM
|
Joined: Jul 2004
Posts: 9,569
Member
|
I would go with the FRN. That will tolerate a short time spike in current. The biggest opportunity for a spike in current is when you have a power glitch and the service would see locked rotor from every motor that was running at that time.
Greg Fretwell
|
|
|
Re: Which Cartridge Fuse?
[Re: gfretwell]
#187499
06/29/09 03:28 AM
|
Joined: Jul 2002
Posts: 8,379
Member
|
Yeah, I agree with Greg. You really need something with a bit of time delay on it for a main fuse. After all, the fuse/CB that is electrically closest to the fault (ie, a sub-circuit fuse/CB) should operate first, in any electrical system. Anything less is poor design.
|
|
|
Re: Which Cartridge Fuse?
[Re: Trumpy]
#187503
06/29/09 11:19 AM
|
Joined: Dec 2000
Posts: 4,287
Member
|
You answered your own question. The heavy-duty time-delay one said it is "for motor and main panel protection. (FRN-R)"
|
|
|
Re: Which Cartridge Fuse?
[Re: Trumpy]
#187509
06/29/09 12:09 PM
|
Joined: May 2004
Posts: 24
OP
Member
|
Thanks for the responses. I shall go with the time delay fuse. (I actually bought two of both types with the intention of returning one pair after I determined which type I should use.)
|
|
|
Re: Which Cartridge Fuse?
[Re: thiggy]
#187517
06/29/09 07:24 PM
|
Joined: Jul 2001
Posts: 599
Member
|
There is almost no reason to ever install an NON fuse. For all intents NONs are old technology, and are almost always sold based on price only.
|
|
|
Re: Which Cartridge Fuse?
[Re: JBD]
#187526
06/29/09 10:36 PM
|
Joined: Jul 2004
Posts: 9,569
Member
|
We used NONs to protect electronics and there was even a faster blowing fuse that we used for the input to switcher power supplies way back when they were a big cabinet full very expensive parts.
Greg Fretwell
|
|
|
|
|