Is this transformer calculation correct? #187389 06/25/09 03:54 PM
Joined: Mar 2006
Posts: 81
B
bigpapa Offline OP
Member
600v 3 phase to 120/208v 150kva dry type isolation transformer.
For some reason I need to be reminded of certain things that I have
forgotten over the years. Maybe someone can refresh me on this
transformer calculation.
Transformer is dry 150kva 3ph 600 to 120/208v isolation type.


Rated primary current is 144.5A
Primary breaker chosen is 150A therefore secondary current is 150x turns ratio of
2.88 which is 432A
Secondary conductors are 125% of RATED secondary current and
not actual secondary current which would be 416.6 x 1.25 = 520.8A.

I am thinking that secondary conductors are not calculated on the basis of actual secondary current but the transformers rated current.
Am I correct or have I missed something here?

Tools for Electricians:
Re: Is this transformer calculation correct? [Re: bigpapa] #187395 06/25/09 07:52 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
This is a 480 volt 3 phase to 120/208 volt 3 phase right??
Also this is a feeder right???
1.73 x 480 = 830.4
150 x 1000 = 150000
150000 divided 830.4 = 180.63 amps primary
1.73 x 208 = 359.84
150000 divided by 359.84 = 416.85

then go to table 450.3(B)

That 600volts on Primary I think might be more like 480 volts.
Yoopers

Re: Is this transformer calculation correct? [Re: Yoopersup] #187398 06/25/09 08:32 PM
Joined: Mar 2006
Posts: 81
B
bigpapa Offline OP
Member
Americans.

Re: Is this transformer calculation correct? [Re: bigpapa] #187401 06/25/09 10:29 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Rule 26-258: 125% of rated secondary current
150,000 / 208 / 1.732 x 1.25

primary conductors are also 125% in the same rule. It's the same calculation except 600 volts is substituted for 208 volts.

The same rule allows you to reduce the size to the demand providing... etc.

Overcurrent rules are in 26-256. Watch the ampacity of panels and splitters fed from transformers. They also must be rated for 125%.

For our Southern friends, 600/347 volts is common in Canada.


Re: Is this transformer calculation correct? [Re: bigpapa] #187403 06/26/09 12:30 AM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
Lets not turn this into some American bashing thing, his calculations are correct for secondary current. Maybe you forgot to use those little icons above each post.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,403 Are you busy
209,295 Re: Forum
196,589 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3