Receptacles near a shower/tub area #186669
05/23/09 12:26 PM
05/23/09 12:26 PM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Here is a question. How close can a receptacle get to the shower/tub area before it is a violation? A foot? 3 feet? 18" Any thoughts? You know that I am going somewhere with this question. I would like to hear some answers first before I bring out the problem I am hearing. Thanks for any answer.

2017 / 2014 NEC & Related Books and Study Guides
Re: Receptacles near a shower/tub area [Re: harold endean] #186672
05/23/09 12:53 PM
05/23/09 12:53 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
A strict reading of the code says it can't be in "tub space". As long as it is outside the shower curtain it is "hold your nose" legal. Good design would put it where water is unlikely to splash on it. These days a nuisance trip of the GFCI is the most likely problem.


Greg Fretwell
Re: Receptacles near a shower/tub area [Re: gfretwell] #186674
05/23/09 04:21 PM
05/23/09 04:21 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Try 406.8(C)2005 N.E.C.

Re: Receptacles near a shower/tub area [Re: Yoopersup] #186678
05/23/09 05:59 PM
05/23/09 05:59 PM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,


As usual you are on target with what I am thinking. I will give it another day or two before I say what is on my mind.

Re: Receptacles near a shower/tub area [Re: harold endean] #186698
05/24/09 11:04 PM
05/24/09 11:04 PM
J
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
As long as it is outside the footprint you are OK code-wise.

Doesn't do much to stop you from plugging in the TV and setting it on the tub ledge tho. I know that hard and fast distances might be hard to achieve in a small bath but there should be a better way.

Re: Receptacles near a shower/tub area [Re: Jim M] #186700
05/25/09 02:56 AM
05/25/09 02:56 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
We put GFCIs in places like this and just hope they do the job when people are stupid.


Greg Fretwell
Re: Receptacles near a shower/tub area [Re: gfretwell] #186714
05/25/09 03:07 PM
05/25/09 03:07 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,041
Brick, NJ USA
Outside of the tub 'footprint' is all I can enforce.

Harold...are you aiming for the flat screen TV issue??



John
Re: Receptacles near a shower/tub area [Re: HotLine1] #186730
05/25/09 09:45 PM
05/25/09 09:45 PM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
As far for tub footprint anything outside of the " boundary line " is fine but if someone really serious about putting a flat tv in the bathtub area one way you can make is safe is breech a opening behind the wall and put in marine grade plexglass and install the flat tv behind I know someone did that allready.

Myself I did not see that setup so hard to say if that did pass with flying colours or Drapeau rouge {red flag} show up.

Merci,Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Receptacles near a shower/tub area [Re: frenchelectrican] #186733
05/25/09 10:05 PM
05/25/09 10:05 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
re plexiglass
France may have some great water, after all you invented bottling it but in most places I would use tempered glass so you could keep it clean.


Greg Fretwell
Re: Receptacles near a shower/tub area [Re: gfretwell] #186734
05/25/09 10:20 PM
05/25/09 10:20 PM
H
harold endean  Offline OP
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I am going where Greg is talking about. What is the tub space? What does 406.8(C) really say? "Receptacles shall not be installed within or directly over a bathtub or shower area." Does sec. 410.4 (which defines a shower area) refer to the shower area? Does it mean a receptacle can't be within 3' of the tub/shower edge?

I have seen many times where someone puts a TV in the bathroom but forgets to make the receptacle a GFI protected one. So they fail that job, but can you fail someone for having a receptacle within 3' of the tub? What is the code section?

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,645 Are you busy
188,780 Re: Forum
178,497 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 16 (0.003s) Memory: 1.0259 MB (Peak: 1.2087 MB) Zlib enabled. Server Time: 2018-11-21 01:49:57 UTC