Receptacles near a shower/tub area
#186669
05/23/09 12:26 PM
|
Joined: Feb 2002
Posts: 2,233
OP
Member
|
Here is a question. How close can a receptacle get to the shower/tub area before it is a violation? A foot? 3 feet? 18" Any thoughts? You know that I am going somewhere with this question. I would like to hear some answers first before I bring out the problem I am hearing. Thanks for any answer.
|
|
|
Re: Receptacles near a shower/tub area
[Re: harold endean]
#186672
05/23/09 12:53 PM
|
Joined: Jul 2004
Posts: 9,569
Member
|
A strict reading of the code says it can't be in "tub space". As long as it is outside the shower curtain it is "hold your nose" legal. Good design would put it where water is unlikely to splash on it. These days a nuisance trip of the GFCI is the most likely problem.
Greg Fretwell
|
|
|
Re: Receptacles near a shower/tub area
[Re: gfretwell]
#186674
05/23/09 04:21 PM
|
Joined: Mar 2003
Posts: 849
Member
|
|
|
|
Re: Receptacles near a shower/tub area
[Re: Yoopersup]
#186678
05/23/09 05:59 PM
|
Joined: Feb 2002
Posts: 2,233
OP
Member
|
Greg,
As usual you are on target with what I am thinking. I will give it another day or two before I say what is on my mind.
|
|
|
Re: Receptacles near a shower/tub area
[Re: harold endean]
#186698
05/24/09 11:04 PM
|
Joined: Aug 2001
Posts: 457
Member
|
As long as it is outside the footprint you are OK code-wise.
Doesn't do much to stop you from plugging in the TV and setting it on the tub ledge tho. I know that hard and fast distances might be hard to achieve in a small bath but there should be a better way.
|
|
|
Re: Receptacles near a shower/tub area
[Re: Jim M]
#186700
05/25/09 02:56 AM
|
Joined: Jul 2004
Posts: 9,569
Member
|
We put GFCIs in places like this and just hope they do the job when people are stupid.
Greg Fretwell
|
|
|
Re: Receptacles near a shower/tub area
[Re: gfretwell]
#186714
05/25/09 03:07 PM
|
Joined: Apr 2002
Posts: 7,233
Member
|
Outside of the tub 'footprint' is all I can enforce.
Harold...are you aiming for the flat screen TV issue??
John
|
|
|
Re: Receptacles near a shower/tub area
[Re: HotLine1]
#186730
05/25/09 09:45 PM
|
Joined: Feb 2003
Posts: 939
Member
|
As far for tub footprint anything outside of the " boundary line " is fine but if someone really serious about putting a flat tv in the bathtub area one way you can make is safe is breech a opening behind the wall and put in marine grade plexglass and install the flat tv behind I know someone did that allready.
Myself I did not see that setup so hard to say if that did pass with flying colours or Drapeau rouge {red flag} show up.
Merci,Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
Re: Receptacles near a shower/tub area
[Re: frenchelectrican]
#186733
05/25/09 10:05 PM
|
Joined: Jul 2004
Posts: 9,569
Member
|
re plexiglass France may have some great water, after all you invented bottling it but in most places I would use tempered glass so you could keep it clean.
Greg Fretwell
|
|
|
Re: Receptacles near a shower/tub area
[Re: gfretwell]
#186734
05/25/09 10:20 PM
|
Joined: Feb 2002
Posts: 2,233
OP
Member
|
I am going where Greg is talking about. What is the tub space? What does 406.8(C) really say? "Receptacles shall not be installed within or directly over a bathtub or shower area." Does sec. 410.4 (which defines a shower area) refer to the shower area? Does it mean a receptacle can't be within 3' of the tub/shower edge?
I have seen many times where someone puts a TV in the bathroom but forgets to make the receptacle a GFI protected one. So they fail that job, but can you fail someone for having a receptacle within 3' of the tub? What is the code section?
|
|
|
|
|