HandHoles N.E.C. 2005 314.30 #186189
04/25/09 07:29 PM
04/25/09 07:29 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
What Teir rating would a Handhole in a sidewalk with foot trafic, EXcept possibly winter plowing??
I Know about ansi/scte 77-2002
Just wondering by Field experience whats common.
Yoopersup

2017 / 2014 NEC & Related Books and Study Guides
Re: HandHoles N.E.C. 2005 314.30 [Re: Yoopersup] #186191
04/25/09 08:16 PM
04/25/09 08:16 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Standards aside .... for ordinary foot traffic, the usual concrete box with the plastic / concrete lid ought to be sufficient. I woukld not choose the all plastic or fiberglass lids.

Re: HandHoles N.E.C. 2005 314.30 [Re: renosteinke] #186214
04/27/09 01:09 PM
04/27/09 01:09 PM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
Though not code, this is what I specify for areas of light-duty pedestrian Traffic only: Fiberglass-reinforced polyester resin, structurally tested according to SCTE 77 with 3000-lbf (13 345-N) vertical loading.

In sidewalk within 5-ft (1.5-m) of a roadway and unprotected from the roadway SCTE 77 Tier 8 (fiberglass unit with polymer-concrete frame and cover. In driveways, parking lots and similar areas subject to occassional loading by heavy vehicles SCTE 77, Tier 15 (polymer-concrete).

I have them set flush in paved or concrete surfaces. Of course I avoid this whenever possible.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,857 Are you busy
184,210 Re: Forum
173,451 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 0.9511 MB (Peak: 1.0774 MB) Zlib enabled. Server Time: 2018-05-22 04:06:51 UTC