#186189 - 04/25/09 07:29 PM HandHoles N.E.C. 2005 314.30  
Yoopersup  Online Content
Member
Joined: Mar 2003
Posts: 830
Michigan
What Teir rating would a Handhole in a sidewalk with foot trafic, EXcept possibly winter plowing??
I Know about ansi/scte 77-2002
Just wondering by Field experience whats common.
Yoopersup


2017 / 2014 NEC & Related Books and Study Guides

#186191 - 04/25/09 08:16 PM Re: HandHoles N.E.C. 2005 314.30 [Re: Yoopersup]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Standards aside .... for ordinary foot traffic, the usual concrete box with the plastic / concrete lid ought to be sufficient. I woukld not choose the all plastic or fiberglass lids.


#186214 - 04/27/09 01:09 PM Re: HandHoles N.E.C. 2005 314.30 [Re: renosteinke]  
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
Though not code, this is what I specify for areas of light-duty pedestrian Traffic only: Fiberglass-reinforced polyester resin, structurally tested according to SCTE 77 with 3000-lbf (13 345-N) vertical loading.

In sidewalk within 5-ft (1.5-m) of a roadway and unprotected from the roadway SCTE 77 Tier 8 (fiberglass unit with polymer-concrete frame and cover. In driveways, parking lots and similar areas subject to occassional loading by heavy vehicles SCTE 77, Tier 15 (polymer-concrete).

I have them set flush in paved or concrete surfaces. Of course I avoid this whenever possible.



Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 