#185449 03/14/09 10:53 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I inspected a Kohler steam unit for a sauna and the directions on the cover for the J-box says 105 wire terminations. Not enough detail for me to go on so I asked the contractor to use 105 wire for the final connection on the unit. Has anyone run into this before? The installation manual is silent on this and the nameplate says use #6 copper wire and install on a 70a. circuit breaker. I don't see a problem with the circuit since it is a heating unit but I guess the contractor is having trouble finding 105 #6 wire.



George Little
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Aug 2007
Posts: 853
L
Member
Isn't all THHN 105 c rated?

Joined: Dec 2000
Posts: 4,289
Member
THHN is rated for 105C only when used in dry locations, when rated AWM, and used as appliance wiring material.

Joined: Jan 2005
Posts: 5,361
Likes: 1
Cat Servant
Member
I have encountered a similar situation with some HID lighting fixtures.

While I can generally come into the fixture with THHN, and use the two-color Scotch wire nuts (which are 105 rated), without trouble .... when in doubt, I place another box a foot or so away from the fixture,and run a pigtail of fiberglass insulated wire. Such wire is available in appliance parts stores.

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I've run into this also, usually with light fixtures. My electrical supplier carries type SA wire which is silicone insulated with a fiberglass jacket, rated 200C for dry locations. It is a little pricey, so I too use a j-box nearby to make the transition. Most wirenuts I've encountered are rated for the 105 degree temperature.


Few things are harder to put up with than the annoyance of a good example.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
Trumpy 9
NORCAL 5
Popular Topics(Views)
300,382 Are you busy
230,030 Re: Forum
214,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5