Immersion Heaters #185058
03/01/09 03:18 PM
03/01/09 03:18 PM
C
clgman  Offline OP
New Member
Joined: Feb 2009
Posts: 2
Boston, Ma
Gentlemen: This question concerns both application and safety(perhaps more) on direct Immersion Electric Heaters in a sump of a Cooling Tower. The Heaters are in direct contact with the water of the sump (cold water basin) to prevent freezing (typically 40 to 45 degrees). The sump areas are typically large enough to access through a door onto a cat walk. This places a worker directly above a sump area with a potentially charged (heater energized and failing) water source. Finally, my questions!! Is there a Megohm reading that the heater should pass to be considered safe, and does or should any type of code call for a specific type of breaker or fuse(circuit protection)for this application ?? More information available if required, thanks.

Work Gear for Electricians and the Trades
Re: Immersion Heaters [Re: clgman] #185059
03/01/09 03:40 PM
03/01/09 03:40 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,252
Estero,Fl,usa
We use immersion heaters everywhere, like spas and domestic water heaters. The case of the element is usually bonded. Generally they seem to be pretty safe. If you are concerned, put it on a GFCI.


Greg Fretwell
Re: Immersion Heaters [Re: clgman] #185060
03/01/09 04:24 PM
03/01/09 04:24 PM
K
kohli  Offline
New Member
Joined: Mar 2008
Posts: 9
Ohlo Putnam Co
You are talking about in cooling towers Just put your lock on the heater disconect if you are concerned & why are you in there to do what?

Re: Immersion Heaters [Re: kohli] #185078
03/01/09 11:23 PM
03/01/09 11:23 PM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
IIRC the cooling towers do have specal safety producres if you used the immerison heaters and yes you must have a disconnection switch if you go in the " restricted " area.

If this on 3 you can get this on GFI relay or GFI breaker it will sense any bad elements that shorting out it will trip the GFI and the alarm luminaire go on to give you a head up the heater malfuction.

Merci,Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Immersion Heaters [Re: clgman] #185169
03/04/09 11:55 PM
03/04/09 11:55 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Originally Posted by clgman
Gentlemen: This question concerns both application and safety(perhaps more) on direct Immersion Electric Heaters in a sump of a Cooling Tower. The Heaters are in direct contact with the water of the sump (cold water basin) to prevent freezing (typically 40 to 45 degrees). The sump areas are typically large enough to access through a door onto a cat walk. This places a worker directly above a sump area with a potentially charged (heater energized and failing) water source. Finally, my questions!! Is there a Megohm reading that the heater should pass to be considered safe, and does or should any type of code call for a specific type of breaker or fuse(circuit protection)for this application ?? More information available if required, thanks.


I think that qualified persons following a written safety procedure can do more to prevent accidents than anything else.

IMO, since you normally can't enter a cooling tower to do any maintenance without first shutting down the water pumps at the chiller location, you should also LOTO the circuits or disconnects for the tower heaters and make up water valve before attempting to clean the sump filter grates or perform algae and mold removal.

Re: Immersion Heaters [Re: KJay] #185290
03/08/09 01:54 PM
03/08/09 01:54 PM
C
clgman  Offline OP
New Member
Joined: Feb 2009
Posts: 2
Boston, Ma
Thanks for the replies, and I understand the normal safety procedures for Lock Out, Tag Out, etc. However to attempt to predict heater failure, or when a heater should be taken out of service before it actual trips a breaker or blows the fuses, a megohmeter reading or hipot test. or some type of test ought to able to be preformed to predict such a failure, and I'm courious about the voltage/current leakage to ground before the fault take place. Thanks Clgman.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,623 Are you busy
186,362 Re: Forum
175,828 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.005s) Memory: 0.9778 MB (Peak: 1.1211 MB) Zlib enabled. Server Time: 2018-08-19 09:43:38 UTC