CRW Offline OP
Member
Are there any scenarios where you can run a flexible cord through a drop ceiling? I was told we could run a cord from a box above a ceiling, through the tile, with a cord connector on the end. This is for an appliance that is in the middle of an institutional kitchen, away from the wall, so we can't use a fixed receptacle. 400.8(2) seems to not permit this, but it also says, "Unless specifically permitted in 400.7..." which could then refer to 400.7(6)&(8). I questioned this whole thing at work (without citing the actual code, I didn't have it with me at the time) but the foreman said it was OK to do. What do you think?

Horizontal Ad
Joined: Aug 2007
Posts: 853
L
Member
400.7 says nothing of passing through ceilings. it speaks to cords for equipment.
400.8 is the guide.

I would install a ceiling box and drop a cord with strain relief and twist lock cap.Don't forget,if it is 120 volt 15 or 20A GFCI is needed. 210.8(B)(2)

Last edited by leland; 02/25/09 07:30 PM. Reason: 210.8
Joined: Jan 2005
Posts: 5,462
Likes: 3
Cat Servant
Member
Passing a cord through the ceiling tile, as you describe, is a code violation in two ways: there's a flexible cord above the grid, and the cord is passing through a partition.

That said ... I recognize that this is often done, and that circumstances often make even a ceiling box impractical. I'm not quite sure where to go with this ... maybe a proposal for the next NEC cycle - but I'm not sure how one would write it.

Drop ceilings, once the 'wunderkind' of building, are quickly becoming a major headache. Perhaps their time has passed.

Joined: Apr 2002
Posts: 7,390
Likes: 7
Member
Another old addage from NJ....

"Drop ceilings hide a multitude of sins"

That said, cord thru the tile is a no-no. A ceiling grid mounted box, suitable coverm strain relief, & TL is accepted

However, a TL recept mounted in the ceiling box, face down, that the cord from the equip plugs into may be a better way.

Some AHJ's cite the cord from the ceiling box in the first scenario as using cord for permanent wiring, and red flag this, absed on 400.7 & 400.8 interpertations.


John

Link Copied to Clipboard
Advertisement:-Right

* * * * * * *
Tools for Electricians
Tools for Electricians
 
* * * * * * *

2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
323,575 Are you busy
247,890 Re: Forum
231,670 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5