ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 646 guests, and 49 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Feb 2009
Posts: 3
R
Rhiney Offline OP
New Member
Hello there!
I've got a situation here where we are setting a 112.5kva480x 120/208 transformer on the roof of a building.
It will supply power to a 400Amp MCB-type panelboard below roughly 40'of conduit and wire away.
Are we required to have a fused disconnect near the transformer (word has it wthin 25')? Where in the code is this requirement if it exists?
Primary overcurrent protection is a 175amp circuit breaker.
Thanks much for any help

Horizontal Ad
Joined: Mar 2003
Posts: 849
Y
Member
240.21
Read which one applys in this section for you.
Also read Table 450.3(B).

Last edited by Yoopersup; 02/14/09 11:44 PM.
Joined: Feb 2009
Posts: 3
R
Rhiney Offline OP
New Member
Thanks much Yoopersup.
That cleared it right up for me . A fused disconnect within 25ft it is .


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,440
Joined: February 2004
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
553,292 Are you busy
427,835 Re: Forum
398,184 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5