#184275 - 02/06/09 12:28 AM Septic pump wiring  
schenimann  Offline
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
What is the preferred method for wiring these? I was at a house today and there was one outside. It had about a 30" cover with the wires coming out the center. They were drapped across then went down into some conduit underground and came up the wall to the alarm and disconnect. I have also seen these where they just bury the wires to the wall and plug them in. How in the world does this pass inpection?

What is the best way to get the wires out of the tub and into conduit?


Work Gear for Electricians and the Trades

#184280 - 02/06/09 02:24 AM Re: Septic pump wiring [Re: schenimann]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Best way?

The arrangement you describe is typical for indoor installations ... but not for outdoor.

Typically, an outdoor unit will have sort of junction box, as there's no way the cables will reach the panel.

"Bargain" installs will attempt to use a box of some sort in the pit. This is a poor choice, as a) the box rusts, and fills with crud; and, b) cables coming in are subject to damage, ensuring a future replacement.

"Better" installs will have a Christy box near the pit, with splices made there. The weakenss with these is that the conduit to the pit is NEVER big enough. Cables swell, and it becomes impossible to pull them out for replacement.

"Best" would be TWO handholes - one for power, one for the floats. 2" pipe would exit using a sweep from under the handhole, and enter the pit farther down. If you wanted, you could even try to seal this pipe with ductseal; I wouldn't bother.

How you get from the house to the handholes is up to you. I would -again- prefer pipe. Now, this pipe I would seal at the handhole - that swelling insulation issue again.


#184283 - 02/06/09 09:21 AM Re: Septic pump wiring [Re: renosteinke]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
As Reno suggests.
I enlarge (or make a new) hole in the 'chimney' of the tank, 2" pvc out for the floats. Pvc from the house to the new PVC box. Too many guys just add a box in the pit and use the factory 1'. My Tummy is too weak for that.

2 ckts out there. 1- for the run/stop floats and 1- for the alarm float.



Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7533 MB (Peak: 0.8791 MB) Zlib enabled. Server Time: 2017-11-17 19:22:41 UTC