210.25(B) #183724 01/20/09 09:21 PM
Joined: Aug 2007
Posts: 853
L
leland Offline OP
Member
210.25. Branch ckts in buildings with more than one occupancy.

210.25(B)- common area branch ckts.
Ma. has an exception:210.25(B)-

"Exception:Branch ckts supplying lighting outlets in common areas on the same floor as a dwelling unit in a new or existing two-family or an existing three-family building shall be permitted to be supplied from equipment that supplies one or more of those dwelling units."

My question: Existing two-family.
If I install interconnected smokes & CO det. (required in Ma.) for both units and common areas (2-family)and the common area lights (same ckt),Off of a tenants panel.
Side by side units 2 floors each. Existing house.(used to be owner occupied).

Would this be accepted?



2017 / 2014 NEC & Related Books and Study Guides
Re: 210.25(B) [Re: leland] #183726 01/20/09 09:46 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
Leland:
Here in NJ, any 'common area' has to be from a 'common area' (house) panel.

Common area definition is rather lengthy; I'll be brief.

Stairwells, hallways, etc common to all occupants. One heating unit for multiple occupants; a 'shared area (basement, etc)

Here, you could not do what you intend above, you would have to install a house/owner meter and panel.



John
Re: 210.25(B) [Re: HotLine1] #183728 01/20/09 09:51 PM
Joined: Aug 2007
Posts: 853
L
leland Offline OP
Member
Understood, That's why I included the "exception", Looking for interpretations.
Here,an over/under situation would not fly. The way I read it.

Re: 210.25(B) [Re: leland] #183742 01/21/09 10:37 AM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
Sounds like it is allowed, since MA Amendment 210.25, exception says branch circuits [plural] and both units are on the same level.
I personally donít like the idea of only one tenant having access to the circuit breaker supplying the smoke alarms for the entire building, even with the battery backups, but it sounds like itís perfectly okay as far as the exception goes.
If the circuit panels were both located in a common area like the hallway, basement or laundry, I wouldnít have any problem with it at all.

Leland: Are the CO alarms now required to be hard wired and interconnected between units in MA, or is this just because it is a single structure with no firewall separation?
Does this mean they are no longer allowing the individual 120V plug-in units with battery backup?


Re: 210.25(B) [Re: KJay] #183749 01/21/09 02:25 PM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
Are smoke detectors "lighting outlets" in Massachusetts?

Quote
"Exception:Branch ckts supplying lighting outlets in common areas on the same floor as a dwelling unit in a new or existing two-family or an existing three-family building shall be permitted to be supplied from equipment that supplies one or more of those dwelling units."


Greg Fretwell
Re: 210.25(B) [Re: gfretwell] #183753 01/21/09 03:33 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
Good point Greg, the exception does only state lighting outlets.

I donít really like the idea of only one tenant having exclusive access to the smoke alarms circuit breaker anyway. If that tenant goes out of town for several days and for some reason the breaker trips, there could be an issue. Also, what happens if they move out and power is turned off to that unit?
I havenít done an existing two family conversion in several years, but the last time I did one, I wasnít allowed to have the two units interconnected. What I was allowed to do was have interconnected smoke alarms installed in each unit, supplied from each units own panel, keeping each unit separate. Then I extended one additional smoke alarm from each unit in each of the common areas, like the hallway, stairway and basement laundry area, basically giving redundant initiation in common areas.
Maybe the rules have changed. If so, it sounds like a house panel might be the only solution, possibly even if installing a low-voltage system.



Re: 210.25(B) [Re: KJay] #183764 01/21/09 09:26 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
Leland:
I read the exception again, and the comments above, and have to say 'No' again.

have you run this by the local AHJ in the town?

As I said, here you would need a house panel & meter.


John
Re: 210.25(B) [Re: HotLine1] #183771 01/22/09 12:10 AM
Joined: Aug 2007
Posts: 853
L
leland Offline OP
Member
New Info to follow:
HotLine, Why NO with the Exception?


KJAY: RE CO Detectors: Hard wired NO, just as simple to add the COMBOS tho, Battery or plug ins' are fine Mandatory since 3/2006- ALL buildings in MA. Government included. 527.CMR.30 Ma. General laws
I was in Falmouth today, Down that far?

Last edited by leland; 01/22/09 12:20 AM.
Re: 210.25(B) [Re: gfretwell] #183772 01/22/09 12:13 AM
Joined: Aug 2007
Posts: 853
L
leland Offline OP
Member
Greg: first point would be a light. Speculation I guess.

Re: 210.25(B) [Re: leland] #183783 01/22/09 09:27 AM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
Does the exception state 'on same floor/level'? IF your job falls under that, then it's OK; but....are smokes considered 'lighting outlets'?? I would think 'no'

Have you checked with the local AHJ?? I'm a Jersey guy, and as I said...it will not fly here. The Fire Sub-Code AHJ would not allow one dwelling unit to provide power for the smokes in a common area. IF the areas are not 'common' such as a stairwell for ONLY one of the units, that is a different story.



John
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician