#183146 - 12/28/08 03:08 PM Class-II,Div 1?  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
I had a discussion the other day with my office, I feel weather tight would meet the code. (existing install is Cls2-div1).
Coal power plant, dock side open conveyer for unloading the barge, Only a shroud over the belt.
My scope: Fire alarm pull stations,120V AC onthe outside railing,notification only to control room. Deluge is manual operation.
The railing is 8' away from the conveyer system,in the wide open air,along the river. All conduit is threaded rigid.
I feel weather tight would be enough.


2017 / 2014 NEC & Related Books and Study Guides

#183155 - 12/28/08 04:26 PM Re: Class-II,Div 1? [Re: leland]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
For the most part, you're correct. There are two situations that bear considering, though:
1) Where there are moving parts. For example, you don't want dust to get within a breaker, and prevent it from operating. There you would be looking for a dust-tight enclosure; and,
2) Where heat is generated. Motors and light fixtures must remain cool enough that they do not ignite the dusts ... even when they are buried in the dust.



Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7446 MB (Peak: 0.8642 MB) Zlib enabled. Server Time: 2017-10-23 08:08:39 UTC