ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 4 of 5 1 2 3 4 5
Joined: May 2007
Posts: 46
Member
I notice now a bit late, that chico gave a much more detailed description of traveler juggling - oops -oh well.

(this makes page 4)

Joined: Aug 2007
Posts: 853
L
Member
I challenge anyone. 1 months time under NORMAL operation to maintain that condition!
It's fun reading, but........ You folks are outa your MINDS!!! I meen that in a good way! smile

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
"All down" = "off" will always be true if you wired it that way.


Greg Fretwell
Joined: Aug 2001
Posts: 7,520
P
Member
I suppose we could install the switches sideways, but then there would be the argument over whether both left/both right = off or one left/one right = off! Still, that's better than ground up vs. ground down I suppose! wink

Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Well, Greg, you and I are going to have to disagree about that one! I've already described -twice- how an installation the starts off as 'down=off' changes the very first time you flip any switch.

I dare say that it's simply not possible for 'down=off' to remain true after the first switch operation.

Joined: Aug 2001
Posts: 7,520
P
Member
I think you two are looking at this from a slightly different perspective.

If you wire so that both down = off, then clearly as soon as you move one switch up you will be left with the situation where the other switch being down will result in the light being on.

But however many times you operate the switches, these conditions will hold true:

1. Both switches down = Off
2. Both switches up = Off
3. One switch up, one switch down = On.

Swap the travelers over at one end only and these three conditions will always hold true:

1. Both switches down = On
2. Both switches up = On
3. One switch down, one switch up = Off


Joined: Jan 2005
Posts: 354
P
pdh Offline OP
Member
Originally Posted by pauluk
But however many times you operate the switches, these conditions will hold true:

1. Both switches down = Off
2. Both switches up = Off
3. One switch up, one switch down = On.

Swap the travelers over at one end only and these three conditions will always hold true:

1. Both switches down = On
2. Both switches up = On
3. One switch down, one switch up = Off


For systems with an odd number of switches (an odd number of 4-way ones), then you have:

1. All switches down = Off
2. All switches up = On
3. Even number of switches up, odd number of switches down = Off
4. Odd number of switched up, even number of switches down = On

Swap the travelers over at one end only and these four conditions will always hold true:

1. All switches down = On
2. All switches up = Off
3. Even number of switches up, odd number of switches down = On
4. Odd number of switched up, even number of switches down = Off

So the design rule choices could be narrowed down to:

1. All switches down = Off
2. All switches down = On
3. All switches up = Off
4. All switches up = On

I'd prefer #1. The reason is because if I ever needed to change the switches when I did not have a means to see what the effect is (e.g. power is out or light bulb is blown) I'd be wanting to turn them to off in almost all cases. In the rare case I want to leave a light on, I can set them all down then set one up.

pdh #183168 12/28/08 11:43 PM
Joined: Aug 2001
Posts: 335
S
Member
After reading thru 4 pages of this (which I am still laughing at), unless I missed something (highly possible at my advanced state of senility), I think I may have found the flaw. I'm one of the anal people who has all the screws north/south & all lights off if all switches are down ... then along came the wife. She wanted the old rotary dimmer on the dining room 3way. Now I'm scr... uh ... out of luck.

Joined: Jan 2005
Posts: 354
P
pdh Offline OP
Member
Originally Posted by Steve Miller
She wanted the old rotary dimmer on the dining room 3way. Now I'm scr... uh ... out of luck.

Is it the rotary aspect she really wants? Or the push-in to turn it on and off?

If all she wants is the rotary, take a 3-way version of the rotary control and connect its travelers together. Then connect those paralleled travelers to the common of a normal 3-way switch right beside it. Then the normal switch travelers are connected in the usual way. Then you will have a dimmer with no on/off effect, and a real switch right beside it that can be oriented with up for on and down for off. That's if you have the space to add a switch next to it.

pdh #183177 12/29/08 12:06 PM
Joined: Dec 2000
Posts: 4,294
Member
Steve,

You're not out of luck.

Dimmers are available (even rotary) in 3 way configurations.

http://www.lutron.com/rotary/?s=17000&t=17200