ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Does NEC 551.71 (F) apply to dwellings?
by BigB - 01/20/23 10:46 AM
Violation?
by HotLine1 - 01/19/23 09:10 AM
Power submeter connections
by HotLine1 - 01/19/23 09:09 AM
AFDD's coming to the UK
by Texas_Ranger - 01/17/23 07:22 PM
Circuit Breaker Lube
by renosteinke - 01/14/23 06:40 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 78 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
I get a lot of flak from the sign community for requiring them to disconnect branch circuits running to abandonded sign installations like neon. Now the branch circuit in the overhead is still connected to the xmfrs and often HV wiring still run to the old neon tube locations and just cut off. Too much work to take all that out...
Any suggestions on citations for doing this as opposed to 'just turning off the circuit breaker'?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
The ".25" articles within various 'low voltage' Articles addresses abandoned cabling, BUT, there is nothing specific regarding wiring that you specify.

Various local property maintenance codes may address your issues directly.

I would try a 1 on 1 conversation with the tenant/owner, and explain the fact that liability could be on there shoulders if someone were to get injured. Stressing that it is a more economical move to have wiring safed-off than getting involved with lawyers/insurance issues.



John
Joined: Jan 2005
Posts: 5,369
Likes: 1
Cat Servant
Member
Just disconnect at the breaker? Or, remove the old wire completely?

I can see that one might wish the wire to remain in place; there will likely be another sign out there someday.

Too many places operate their signs at the breaker, though, for me to be comfortable leaving the wires hooked up. Often the panels have markings by the breakers saying something like "On at night" or "Off at Closing." It's too easy for the remodelling crew to just flip everything on when they want light.

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
I like the "disconnect at the breaker" idea too. It prevents accidental energizing of the circuit but makes restoring the service easy if they restore the sign.


Greg Fretwell
Joined: Dec 2000
Posts: 4,291
Member
Disconnect it at the breaker and tag it "Abandoned Sign Circuit".



Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
I agree with the commentary but my question is can anyone point to a code or industry standard citation that requires action be taken other than turning off the breaker?

Joined: Jan 2005
Posts: 5,369
Likes: 1
Cat Servant
Member
Congratulations! You found the "loophole!"

For some silly reason, the NEC requires nearly every sort of abandoned to be removed, or capped off and identified at both ends ..... except power wiring.

Don't misunderstand me, we're not talking about an exception that mentions power wiring; we're saying that the NEC simply fails to mention this little detail in the "older" parts of the code.

Blame it on the educational system. When the part about power wiring was written, it was probably assumed that any moron could figure out that you didn't want live wires dangling in the ceiling. Later, when the NEC began to address 'low voltage' trades, standards had changed, and it was realized that it was, in fact, necessary to spell this out. Alas, the never want back and added this to the power wiring sections.

Panel ID is a wonderful thing - I've gone so far as to mark panels in Chinese as well as English - but we all know the limitations of panel ID.

There's probably no law or code saying you can't hang a sign upside down .... but, as with dangling hot wires, I wouldn't think very well of someone who did that.

(You think I jest? I have a customer, a mini-mart, who found several signs mounted upside down when he bought the place. It seems the former owner had literacy issues! laugh )

Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
Perhaps in one of the upcoming code revisions this may be brought up (again).



John
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
Hotline, do you have a specific proposal you are referring to?

Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
JES:

Short & sweet...adding a ".25" to the power wiring and closing the loophole Reno stated above.

Common practice by 'most' EC's is to remove or safe-off power wiring, but...it's not mandated within the NEC.



John

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,341 Are you busy
231,742 Re: Forum
216,370 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5